Shear Wall Without Shear
(This is strictly a theoretical topic. I would never design a shear wall assuming it takes no in-plane loading.)
My question is this: is it theoretically possible, by analysis, that you could have a shear wall supporting a rigid diaphragm and determine that the wall takes a shear force of zero? In other words, could the torsional shear be equal and opposite the direct shear, causing a net force of 0?
Has anyone ever run into this issue when reviewing analysis results from RISA, RAM, Enercalc, Etc? I like that enercalc includes the option to neglect torsional forces when they reduce the shear. It would be nice if this work possible to incorporate into other analysis packages.
RE: Shear Wall Without Shear
Yup. Near zero and sometimes opposite direction. Darn near anything is possible with a rigid diaphragm. If your walls are yielding under seismic demand, and your model considers the wall to be infinitely elastic, that will sometimes change the situation a fair bit.
The accidental torsion may happen on both side of the center of mass, causing reversal of torsion component !
So, in my opinion, it is not possible to have a monolotic wall taking no shear at all in a design point of view.
EDIT : In a single elastic analysis though, you may get a zero shear but it is probably not the combination of load causing maximum shear in the wall. See explanation above.
Just for good measure I often run another analysis without the eccentricity just to see how things are otherwise behaving.