VSD Cracking and Smoke presence
Hi I got this issue occur during the first power on of the vsd there is a cracking then smoke comes out from the device then breaker trip. What could be the possible reason why this issue occur. It could be earth to phase short or IGBT/Thyristor as well.
RE: VSD Cracking and Smoke presence
There could be lots of reasons but one thing is certain. It's stuffed.
Ashtree
"Any water can be made potable if you filter it through enough money"
One thing you can do now however is to confirm the presence or absence of any major misapplication or installation error, for example the wrong voltage or a grounded connection. Beyond that, you replace the unit and start over, send the burned unit to the manufacturer for a Root Cause Failure Analysis (RCFA).
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
Take a look at the electrolytic capacitors for obvious damage.
Bill
"Why not the best?"
Jimmy Carter
SceneryDriver