Hi,

I have a scenario at the expansion joint of building where 4 columns meet. These columns are supported on spread footing (I would rather call it a mat foundation). The foundation is 2m deep and the spacing between the columns 750mm. So, the punching perimeter for individual columns over lap from the other columns. Can I assume the perimeter for punching shear and the one-way shear as shown in the image below. Is there any source which talks about such situations?

RE: Punching shear and one-way shear for closely spaced columns

Both Eurocode and ACI code provide good principles in their corresponding chapters regarding punching shear resistance.

Jason McKee
proud R&D Manager of
Cross Section Analysis & Design
Software for the structural design of cross sections
Moment Curvature Analysis
Reifnorcement Design etc.

RE: Punching shear and one-way shear for closely spaced columns

(OP)
Do ACI provide guidelines when columns are close to one another? If yes, can you guide me where to find it?

Thanks

RE: Punching shear and one-way shear for closely spaced columns

Codes can't cover everything. I think your assumption is valid, provided the column loads are of the same magnitude. With a 2 m deep footing and if your plan is to scale, you probably don't have much in the way of flexural behaviour, and the design is best approached using strut and tie methods.

RE: Punching shear and one-way shear for closely spaced columns

Actually, all codes do cover this.

As an oldish professor I know well would say, Engineering judgement is required in the application and interpretation of design codes!

It is not flexural, it is a deep beam/strut tie condition. There is no punching between the columns, only possibly for the whole group depending on the edge distance from the group. Treat it like a pile cap!

RE: Punching shear and one-way shear for closely spaced columns

(OP)
Just for my understanding, if the footing was like 500mm deep and if the columns were still placed in such a way that the punching shear perimeter coincides, how do you tackle these situations? Is the image I have posted above is the way to go?

RE: Punching shear and one-way shear for closely spaced columns

Further to hokie's point (I think), I'd be inclined to design the combined punching perimeter for four times the load of the most heavily loaded column applied concentrically. That way, you'll have a little extra left in the tank to cover load cases where disparate column loads would produce a moment needing to be resisted by the punching surface. If that method become too punitive for footing depth, consider a more sophisticated analysis. Lastly, I'd make sure that each column would work for punching based on it's own perimeter in the absence of the other columns.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Punching shear and one-way shear for closely spaced columns

Quote (BAGW)


Is there any source which talks about such situations?

This is similar to the punching shear check required for a pile cap. Have a look at CRSI's design guide on pile caps. In short, you check different perimeters for different combinations of axial loads. For your case, I believe the full perimeter for all 4 columns will control.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources