Puddle Flanges--Combining piping penetration together

Puddle Flanges--Combining piping penetration together

Puddle Flanges--Combining piping penetration together

(OP)
Hi All,

I have dyke wall & we are running 4 lines bunched & running together however, I am not sure whether we can have combined penetrations through 300mm thick wall considering required sleeves & puddle flanges?

I do not think so still want to confirm.

I think we should run these lines separately because of the Dyke wall penetrations. This will give way for sleeve pipe, puddle flanges etc.

Is there any other way of having combined penetration? Has anybody done that where sleeves & puddle flange arrangement is must?

RE: Puddle Flanges--Combining piping penetration together

A drawing would help a lot here as would sizes of pipes, type of wall (concrete? brick? earth?)

you can either create an oblong hole and then have a single plate with multiple entries or space out the penetrations.

Is this an new wall being built at the same time or an existing wall?

What is the dyke containing? will it be always liquid or is it a tank bund? What are fire requirements?

You can do most things, but which one is best in your circumstances is very difficult to say with the information provided so far.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Puddle Flanges--Combining piping penetration together

to prevent leakage around each separate hole, as indicated above, a single long dyke plate is best. If separate small plates are tried, the water (trapped fluid) would simply be finding its way past the many divisions between the four separate plates.

However, if the four pipes would ever be at different temperatures or under different stresses (movement) as they move fluids in and out of the tank and the tank expands and contracts, then this movement needs to be anticipated and allowed for between the one single plate and the 4x different pipes penetrating it. This movement can be allowed for in the seals and joints, it just needs to be anticipated.

RE: Puddle Flanges--Combining piping penetration together

These people have been providing seals just for this purpose ..... for decades !

THUNDERLINE Link Seals.

http://www.pipelinesupplies.com/UserFiles/File/Pip...

let us know about your final solution ....

MJCronin
Sr. Process Engineer

RE: Puddle Flanges--Combining piping penetration together

(OP)
racookpe1978 thanks for the guidance however, any rough sketch of what you have mentioned will be a great thing to understand this. My worry is does this arrangement is leak proof?

Thanks & Regards,
Abhijit

RE: Puddle Flanges--Combining piping penetration together

The alternate method is to have the piping ran over the dike wall if its only 4' to 5' high.

RE: Puddle Flanges--Combining piping penetration together

The issue you need to determine is whether you can effectively anchor the pipes at this location. IF you can then you simply weld the pipes to the plate or use a puddle flange / anchor flange but all welded into one plate or cast in situ. See pictures below for what I mean.

However if your pipes need some flexibility to avoid overstress, then you need to use sleeves and then seal.




Note that in the buncefield tank farm fire, the seals through the bunds where sleeves were used failed after a few hours of exposure to fire and led to massive issues with leaking tank bunds and polluted fire water. Seals do not have the fire resistance that welded plates or concrete walls with embedded flanges have.

Not having any penetrations through a bund wall is better, but can create issues with drains.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Puddle Flanges--Combining piping penetration together

(OP)
This is great help LittleInch, thanks for the same.

I see these separate penetrations for each line spaces out as per the requirement which possibly would be the best way to achieve the requirement & have minimum leakage issues in case of mishaps.

In our case we are going with sleeves to have flexibility. We will typically avoid anchors at penetrations.

I am amazed to get so much of help from this website. Thank you all who are contributing to this forum.

Thanks & Regards,
Abhijit

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources