INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Jobs

ACI 318-11 Section 11.4.6

ACI 318-11 Section 11.4.6

(OP)
A question has come up in our design of a cut and cover subway station. Can walls be exempt from minimum shear reinforcement requirements of section 11.4.6 even though not specifically mentioned in the exemptions? Some say no because they are not specifically mentioned, however they are similar to slabs and footings mentioned in exemption (a) except vertical. They have the same two way action and loads can be shared between weak and strong areas.

RE: ACI 318-11 Section 11.4.6

See if this makes sense:

1. Section 11.9 applies to walls.
2. Section 11.9.1 states that walls with shear perpendicular to the face be designed per 11.11
3. Section 11.11 is the provision for slabs & footings.
4. Section 11.11 refers to applying 11.4 for shear.
5. Section 11.11.3.1 requires you to determine Vs (if needed per Eq. 11-2) from section 11.4

From the above it appears that the ACI logical flow would suggest that walls are to be designed similar to slabs and footings and thus 11.4.6 would apply.

However, having said all that, I always thought that the reason you were exempt was not because the slab or footing was able to distribute loads around but rather that these elements are most always situated on top of soil and thus pose a lower risk of catastrophic collapse that can occur via shear failure in more elevated structural elements.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close