Motor starting voltage dip (MV)

Motor starting voltage dip (MV)

Motor starting voltage dip (MV)

(OP)
I am performing a motor starting study on a 2000 HP motor (4.16 kV), I wonder how much bus voltage dip is allowed in general?

As I remember, NEMA recommendations that the motor terminals voltage during starting shall not dip beyond 85%, what about other connected auxiliary loads? MV/LV Transformers supplying BOP loads? 10%?

RE: Motor starting voltage dip (MV)

That depends on the other loads. Some sensitive electronic equipment cannot take even a 5% dip. Most large power equipment is built to handle +-10%, but remember, the dip transmits through all transformers etc., so a 15% dip in MV becomes a 15% dip at the lowest voltages on the same grid, including those sensitive electronic devices.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: Motor starting voltage dip (MV)

Hi Power0020,

if you want to be on the safe side no more than 10%, aux no more than 3%.
Moreover, check the motor's torque curve and the load curve.

RE: Motor starting voltage dip (MV)

(OP)
Thanks jraef & LDKGR, I am a bit worried about the pickup voltage for undervoltage relays as it may cause a nuisance trip.

ITIC curve can be helpful for electronic equipment against the acceleration time of the motor.



RE: Motor starting voltage dip (MV)

Quote (Power0020)

I am performing a motor starting study on a 2000 HP motor (4.16 kV), I wonder how much bus voltage dip is allowed in general?

As I remember, NEMA recommendations that the motor terminals voltage during starting shall not dip beyond 85%, what about other connected auxiliary loads? MV/LV Transformers supplying BOP loads? 10%?
The formula is: %VD = LRM/F x 100, where: LRM = locked rotor MVA of your motor and F = the maximum available fault current at that point where the motor will be located.
It's been posted here a long time ago. Here's the LINK.

RE: Motor starting voltage dip (MV)

Tried editing but I don't know how.

BTW, the definition of F should read: F = the maximum available faukt "MVA" not "current".

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources