How to Connect NGR with transformer?.Please explain with the process..
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
How to Connect NGR with transformer
|
RE: How to Connect NGR with transformer
The NGRs can be supplied from both of these companies but PowerOhm also makes power resistors for NGR uses.
Neutral conductor between the transformer and NGR to have system insulation rating and warning signs are required on the NGR to notify personnel that it may rise to Phase-to-ground voltage level under fault conditions. In Canada Neutral conductor must meet minimum #8 AWG as per CEC requirements. Grounding conductors as required (I never have thought, but I would say minimum #8 AWG also ?).
RE: How to Connect NGR with transformer
RE: How to Connect NGR with transformer
RE: How to Connect NGR with transformer
You can still have phase to neutral loads with a NGR.
RE: How to Connect NGR with transformer
RE: How to Connect NGR with transformer
Under IEC rules it is permissible if the neutral is broken by switches and circuit breakers.
Under US / Canadian rules, no phase to neutral loads are permissible. Typically there will be isolation transformers for lighting loads in facilities with an NGR.