Fault Location for Phase to Phase Fault

Fault Location for Phase to Phase Fault

Fault Location for Phase to Phase Fault

(OP)
When calculating the fault impedance for a C-A phase fault I am taking Vca/Ica to get Zca ( I am also assuming zero fault resistance). Is that the total loop impedance or is that the one way impedance to the fault? It seems to be the loop impedance to me but from what sources I have read they all imply it is the one way impedance.

RE: Fault Location for Phase to Phase Fault

ZT = TOTAL IMPENDANCE

VA = VC - IC*ZT
VC = VA - IA*ZT

VA - VC = (VC-VA) - (IC-IA)*ZT

2*(VA-VC) = -(IC-IA)*ZT

2*(VA-VC) = (IA-IC)*ZT

2*(VA-VC)/(IA-IC) = ZT

VAC/IAC = ZT/2

ZT/2 = half of the total loop impedance

RE: Fault Location for Phase to Phase Fault

(OP)
Thank you for the clarification I understand now.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources