Heat transfer in water heater
I have an interesting problem that I am struggling to solve.
I am working on a residential project in which the client would like to install a 100L water storage heater to provide hot water to a shower. The hot water heater has 2No. 6kW elements and the water flow required is 0.15 L/s to the shower. Assuming the mains cold water supply is at 10 degrees C and stored water is at 60 degrees C with a mix at the shower head of 38 degrees C how do I work out the amount of time the hot water will last at 38 deg C and what will be the steady state temperature of the hot water supply when the tank is exhausted?
Please humour me.
Bill
Please humour me.
Bill
RE: Heat transfer in water heater
Worst case scenario is where the heater doesn't do anything, which should be easy to calculate
Assuming no losses, the power divided by the specific heat divided by the flow rate gives you the best case steady state temperature.
TTFN
homework forum: //www.engineering.com/AskForum/aff/32.aspx
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers
I know the water heater has a small capacity, but this is what the Client has suggested (for a one bed holiday lodge). I need to have the facts before I go back to him and and tell him it's only going to last 20 mins (or whatever).
My calcs show that the ratio of hot to cold is 127% i.e. 127/100 = 1.27:1 does anyone else concur. So for 0.15L/s; 0.083L/s is hot and 0.66L/s is cold? Therefore the 100L should last 1204 seconds = 20 mins.
Also I have worked out from Q = mCp delta T that the steady state is approximately 20 degrees C (19.57). What I can't get my head round is what effect the constant heating of the water has on the length of time the water will last.
I've ignored all losses because it would drive me insane.
By the way I'm an electrical engineer so please bear with me. It's new territory for me.
Many thanks
TTFN
https://www.youtube.com/watch?v=g6xfQ7ho8BM
John R. Baker, P.E.
EX-Product 'Evangelist'
Irvine, CA
Siemens PLM:
UG/NX Museum:
The heater manufacturer will have data on the hot water capacity (minutes of flow versus flow rate before output temperature drops), and for recovery time (time for the tank to come back to full temperature).
TTFN
Please confirm that there is NO "bathtub" that needs hot water. A shower requires a continuous supply of hot water, but if it turns cooler, the user will "only" get mad and turn off the water. He or she can turn down the cold water side as the supplied water runs colder and colder. A shower in a single room bathroom is probably "only" going to run for those 20-25 minutes, and there probably won't be another shower or another use for hot water while it is running. (A bathtub needs to be completely filled with hot water, and other hot water taps might be running at the same time.)
Any dishwasher or clothes washer running also?
I think your 20 minutes is pretty much it; under the worst-case scenario, the user will continually adjust their shower valve to deliver a constant number of joules to the shower head, which will deplete the heat storage according to the calculation earlier
TTFN
All other shower start times will be between the turn on and turn off temperature.
Further, whatever the starting temperature is, it won't be that for long.
As hot water leaves it is replaced with cold water. Water temperature leaving the tank will not be constant.
So the limiting point is when the water leaving the tank reaches 38C. At that time 100% hot and 0% cold is required.
My approach would be:
Pick an initial tank temperature.
Compute mix for the first liter at the shower head, or first minute under the shower head.
Compute new tank temperature.
Loop until tank temperature = 38
This may provide some help -
http://www.watlow.com/reference/files/powercalcula...
http://www.watlow.com/reference/files/wattage.pdf
Hot water systems take hot water from the top of the tank and admit cold water to the bottom. With a well designed system there is surprisingly little mixing.
Steady state temperature (at the reduced flow rate of 0.084 l/s) is 44 deg with 12 kW or 27 deg with 6 kW. So if no mixing occurs and 12 kW is available at the inlet (doubtful), the shower will operate for 20 minutes as stated, at which point the hot water supply drops from 60* to 44* and the shower mix will need to be adjusted to 0.124 l/s hot - 0.026 l/s cold. The 44* water in the tank then lasts another 13.5 minutes before dropping to 34*.
je suis charlie
I know that's it's a bit of a strange situation, but the Client has asked us to investigate it. Just to give you the whole story, it's a single bed holiday lodge with no kitchen. It has only a shower and WHB, hence he thinks that the load will be low. But inevitably, someone will go in the shower for 20 minutes, run the hot water supply down and the next person has a refreshingly cold shower.
I was trying to show this in actual numbers to the Client to encourage him to put an electric shower in with a small instantaneous undersink heater, so they will never run out of hot water.
When you're paying $600 per night no hot water will not be welcomed with open arms.
Many thanks for all the input, I feel confident that I can put the lid on this one now.
In a home there is hot water needed every few hours, so storage isn't a big loss, but in your case it is different.
The inline tank-less water heaters tend to consume more than the 12KW you mentioned A 13kw tank-less heater will give will give you about 6.5 liters per minute. If this is not enough flow for your shower you would need a bigger unit, and god forbid you have a bath tub there, it would take you half an hour to fill with the 13 kw direct heater.
B.E.
You are judged not by what you know, but by what you can do.
IF this room in inside a house in colder climates, then the "lost heat" from the water heater would offset the need for heating energy when the room is unoccupied. (Like leaving a light on, the lost heat from the water heater will keep the unoccupied room warmer than no heat or lights at all.)
Is that offset enough to pay for the electric power used when nobody is inside?
My summary? At 600.00 per night, your guest WILL DEMAND plenty of hot water for as long as they want to run the hot water. NO compromises will be accepted, and at 600.00 per night, word-of-mouth is fast and very damning.
Home Depot sells the 18 kW unit for $430: http://www.homedepot.com/p/Rheem-EcoSense-RETE-18-...
TTFN