230/115 kV power transformer neutral terminations

230/115 kV power transformer neutral terminations

230/115 kV power transformer neutral terminations

(OP)
a 230/115 kV power transformer has two neutral points brought out through oil/oil bushing similar to phase connections.

The cable compartment interface is similar to phase ones though the neutral points will be solidly earthed and no HV is supposed to appear on these points.

To save some money, Utility proposes to use "dummy" terminations just for oil sealing, or to ask the transformer manufacturer to modify the compartment base plate to contain a LV cable connection (oil-sealing gland?) enabling to terminate a 240 sq.mm cu LV grounding cable.

I have not been dealing with this type of connections before, any clue?

RE: 230/115 kV power transformer neutral terminations

We generally use LV cables for grounding the neutral of ATRs and shunt reactors; however according to IEC 60076-3, the neutral bushing should have an highest voltage for equipment (Um) equal or higher than 17.5 kV, allowing for applied voltage testing at 38 kV or above.
As a consequence we use standard MV (oil to air) bushings for neutral, and connect a couple of LV cables from neutral bushing terminal to the ground (see attached imagage).

Si duri puer ingeni videtur,
preconem facias vel architectum.

RE: 230/115 kV power transformer neutral terminations

During transformer insulation testing, you need the ability to lift the neutral connection to ground and apply 10 kV test voltage to the winding. We have medium voltage bushings on all of our 230/115 kV transformers.

RE: 230/115 kV power transformer neutral terminations

Normally such neutral ends are taken out at the top cover through plain oil to air bushings and connected to station earth grid through copper strips or galvanized steel trips over pin insulators on tank side. It cannot be taken out through plain cable glad as at the time of testing at factory over voltages will appear at this point and suitable bushing to cater this voltage level(min 28kV AC) is to be provided.

RE: 230/115 kV power transformer neutral terminations

All of ours have medium voltage bushing with a bare ground conductor connected to the pad at the top of the bushing. It's necessary to be able to disconnect as mentioned above, so you can't have a direct cable connection through a gland in the transformer housing.

RE: 230/115 kV power transformer neutral terminations

(OP)
I agree about that a MV bushing or terminal should be provided. However, the manufacutrer provided a 115 kV rated bushing, cable compartment and associated cover plate. Don't really know why we have to provide a 115 kV plug termination for a neutral point?

RE: 230/115 kV power transformer neutral terminations

Did your specification call for the ability to run the transformer with a floating neutral? One nearby utility purchases 115/12/12 kV ungrounded wye/delta/grounded wye transformers. On these transformers, the 115 kV winding is fully insulated with a 115 kV neutral bushing.

RE: 230/115 kV power transformer neutral terminations

(OP)
No, spec ask for solidly earthed

115 kV ungrounded wye? Never saw that.

RE: 230/115 kV power transformer neutral terminations

@Power0020, they do make wye ungrounded, delta, wye grounded transformers for a zero degree phase shift. Although I am more accustomed to seeing delta zig-zag where a zero degree phase shift is needed with a symmetrical neutral reference.

RE: 230/115 kV power transformer neutral terminations

(OP)
@Mbrooke, I wonder about running on 115 kV ungrounded, faults will cause very high overvoltages on healthy phases.

RE: 230/115 kV power transformer neutral terminations

Power0020,
the most effective solution is to ask to the transformer manufacturer to modify the neutral bushing, installing a MV oil-to-air bushing. Which kind of neutral bushing was required in the spec?
By the way 110 (or 115) kV sub-transmission networks in central Europe (typically Austria) often used resonant neutral grounding, so that the neutral is always fully insulated.

Si duri puer ingeni videtur,
preconem facias vel architectum.

RE: 230/115 kV power transformer neutral terminations

If you are sure that system is solidly grounded, you can use LV cable for earthing the neutral cable pot head. Probably 110 kV neutral take out is provided to take care of over voltages during factory testing.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources