abb calor emag Is limiter problem

abb calor emag Is limiter problem

abb calor emag Is limiter problem

(OP)
hi
we have abb calor emag Is limiter in a power plant to eliminate short circuit level
it consists of a main conductor (bursting tube) and in parallel hrc fuse
what is the benefit of the fuse ?
are there another companies makes this technology ?
are there another companies can repair a defected one neither abb calor emag?
thanks

RE: abb calor emag Is limiter problem

(OP)
thanks mgtrp
but are there companies can repair a defected Is limiter of abb calor emag?

RE: abb calor emag Is limiter problem

ABB Only.

Clip is not same technologies, Clip is Fuse, Is is operated on di/dt principle.

RE: abb calor emag Is limiter problem

ABB Only.

Clip is not same technologies, Clip is Fuse, Is is operated on di/dt principle.

RE: abb calor emag Is limiter problem

The two are very similar - they both consist of a main conductor in parallel with a fuse. When a fault is detected, a small explosive charge is triggered, rupturing the main conductor and forcing all of the current through the parallel fuse, which quickly blows.

Unless they've made some changes to the triggering algorithms in the ten years since I last had much to do with these devices, the CLiP device is triggered by magnitude of current only, while the IS-limiter includes rate of change of current.

RE: abb calor emag Is limiter problem

(OP)
what is the benifit of the fuse as the main conductor is ruptured first ?
what is the time required for Is limiter to clear the fault ?
thanks

RE: abb calor emag Is limiter problem

Hi Mohammad,

during normal operation only the main conductor is carrying current due to its lower resistance, thus drastically reducing losses within the fuse.
After having ruptured this bypass with the help of an explosive charge the resulting arc reverses the ratio of resistance in favor of the fuse.
The current commutates to the fuse, the arc in the bypass dies and the fuse is blown.
You may find some more detailled description when googleing 'calor emag is limiter'; ABB documents are to be found right above the link to this very forum.

Have fun

Johannes

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources