is hilti anchor bolts capacity software reliable?
Just done a calc of foundation anchor bolts using hilti online software. The hilti bolt capacities (based on combined cone pull out) appear much higher than the Ec code capacity (based on bond stress between anchor an concrete). Is the hilti software reliable?. Been looking at previous discussions on this issue on the forum . Got mixed views. Any advise please?
RE: is hilti anchor bolts capacity software reliable?
Hilti's tech department is fantastic at helping out. Talk to them, express your concern and see what they have to say about that.
A couple of findings from my limited experience:
I have checked their anchor bolt (epoxy and mechanical) capacities to my hand checks using ACI Appendiz D, and there were situations where they were using higher modification factors yielding a higher capacity than what I had calculated. I was able to reconcile this with the fact, that ACI states that other values may be used if certain tests have been completed. Hilti does a very good job of testing their products, and you can contact them if you would like these reports as I did.
As far as how the loads are distributed to the anchor bolts, Hilti assumes a perfectly rigid baseplate. This is fine for most cases, but I have had to deal with some unique/high load cases in which I needed to model my baseplate in FEA in order to determine the loads on the anchor bolts.
Mike McCann, PE, SE (WA)
@msquared48, What is the Simpson?
@KootK thanks for the attached document, does clarify the Hilti elastic theory for anchor bolts, very well explained. I do have a spreadsheet for combined bending and axial force for columns so will tweak the spreadsheet with the hilti approach to see to if I can replicate the Hilti software output.
thank you all!
I fully agree here. A lot of engineer were badly applying correction factors such as edge factor using table when calculating resistance manually.
The result is when using the software, resistance of often so much lower than (wrongly) expected.
Note that the LRFD transition to anchorage bring lower resistance to some failure mode.