location of zone control valve
location of zone control valve
(OP)
hi every one,
Is the NFPA permits to collect all zone control valve for all floors in the same location??
please advice,
regards.
Is the NFPA permits to collect all zone control valve for all floors in the same location??
please advice,
regards.





RE: location of zone control valve
However, this needs to be coordinated with the fire alarm system, because the fire department (and others) will want to know where the fire is happening, which having a single control valve will not facilitate.
RE: location of zone control valve
RE: location of zone control valve
Once you get to 4 floors, that typically requires standpipe (assuming that the top floor is >30' above fire dept access), so then the valves are just located in the stairwell coming off the standpipes.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...
RE: location of zone control valve
RE: location of zone control valve
You need to read NFPA 13 (2013 edition) and then tell us about your building. We're not your consultants.
RE: location of zone control valve