substation bus structure using STAAD
2

substation bus structure using STAAD

substation bus structure using STAAD

(OP)
I am working on a single-phase bus support for a substation. I am trying to model the insulator in STAAD. The insulator is made of porcelain material and rest on top of a HSS column. What is the best the best way to model the insulator in STAAD so that the loads for the bus items sitting on top of the insulator are transferred to the HSS column. What type of member should be used for the insulator? Should the insulator be treated as a dummy member? Any suggestions/comments are appreciated.

RE: substation bus structure using STAAD

You caught me just a couple of years too late! I used to model insulators on substations in STAAD and I'm try to remember how we modeled them. This was for STAAD dynamic analysis. I think we used a fictitious material but my memory is vague. I remember that we modeled insulators as actual members. If I have a memory flash, I'll get back to you.

RE: substation bus structure using STAAD

(OP)
@ BUGGAR That would be helpful if you remember. Thanks

RE: substation bus structure using STAAD

I treat it as a dumb/fictitious element. Then using vendor information verify that it can carry the required loads. I use Risa 3D.

RE: substation bus structure using STAAD

As I remember, you had to get the right EI in the insulator member to simulate the frequency? Develarde, are you doing the dynamics in Risa? I was using '97 UBC dynamic at the time.
I remember everybody that saw the STAAD files immediately saw the "weird" member and flagged it. I'm searching old STAAD files now.

RE: substation bus structure using STAAD

I'm not sure if I get the picture of what is going on or not.....but if you don't need any stresses/other info on the "insulator", why not go ahead and do it's job and put the loads where they go into the HSS column?

RE: substation bus structure using STAAD

Agreed, unless you're doing a dynamic analysis, just model it as a rigid dummy member or bypass it entirely and apply the loads at the base of the insulator.

RE: substation bus structure using STAAD

(OP)
My objective is to design the steel support structures, as far as insulators are concern I have already modeled them. However, I am trying to figure out a way by which I can transfer all my forces (dead load, ice load, short circuit load, insulator load, wind load) onto the HSS Column from 6” Aluminum pipe. Can I use insulator as a dummy member? If so, how can I depict that on STAAD. Also will the force be transferred correctly if I use a dummy member for insulator (REFER TO ATTACHED SKETCH).

http://files.engineering.com/getfile.aspx?folder=3...

RE: substation bus structure using STAAD

If you aren't worried about how the insulator will perform stress wise (or otherwise) and all you need it to do in the model is transfer loads and design the steel....I'd just take a shot at the material properties of the insulator and make it a active member. I say that because I don't think you are going to be able to get the loads from that aluminum pipe to that HSS without an active member. (We may be mixing up our terminology here: some people call a "dummy" member in STAAD one that has a high E value but no density (for the purposes of constraint or load transfer).....but it is an active member IIRC.)

RE: substation bus structure using STAAD

Fuzzy memory says it is an active member with a special EI, or density, or?

RE: substation bus structure using STAAD

Absolutely, by dummy member I mean a geometrically correct rigid link -- still active in the model. Sorry, not familiar with STAAD to know if I'm getting the terminology right.

No offense, but substation steel design (IMO) isn't about getting the most precise answer to your problem. It's about developing a reliable, repeatable, constructable design. Way better to use a standard robust detail than it is to save 2lb/ft on a beam.

Besides, you are likely overestimating your knowledge/modeling of how each individual structure's foundation will behave anyway. For a bus support, you're probably on a bunch of individual drilled shaft foundations -- they're each going to settle and rotate differently from the next. That's likely going to affect your design as much as the properties of an insulator.

Is this really a single column bus support? Why bother with STAAD? Design it by hand and be done.

(All of the above comments assume that you don't need a specific dynamic analysis. And I mean really need -- it'd have to be a complicated substation retrofit or a high seismic zone with substantial space constraints before I'd get to the level of properly modeling insulator behavior.)

RE: substation bus structure using STAAD

For what it's worth, the last few California quakes damaged a lot of electrical equipment and so most of the SoCal utilities (SDG&E, PG&E) all do the dynamic dance. Loss of power to customers is a big deal with them so they are a little different from other industries. And they operate on our dollars so we need'nt be concerned with that.

RE: substation bus structure using STAAD

Buggar, it makes sense that SoCal utilities would be interested in seismic resiliency. What is the result of your dynamic analysis? Refined loading on manufactured components? Minimum clearances to prevent arcing during seismic events?

RE: substation bus structure using STAAD

I just did the structures that hold everything up. The electrical guys give me all the clearances from busses and similar that they need and I make sure everything stays that far apart during an earthquake. I recall all the manufactured things were seismically qualified and we had the masses and frequencies of the assemblies that we could plug into the appropriate node of STAAD.

RE: substation bus structure using STAAD

Hmm.. That's what I was guessing. I would have guessed it would be more intuitive to just space your conductors further apart and not worry about the nitty gritty of dynamic deflections. But most of the substations I worked on were in Kansas and Oklahoma... land is slightly cheaper there.

RE: substation bus structure using STAAD

And remember, this is California where it is wise to cover your shareholders legally by carefully following Codes. Our documentation of design was treated like a holy chalice and carefully filed away in their vault.

RE: substation bus structure using STAAD

If you are worried about the deflection in the 6" aluminum bus tube, you need to model the insulator as a pipe but change the E to whatever the manufacturer of the insulator says it should be to get the deflection right. I use GTSTRUDL to model the bus supports and I am not very familiar with STAAD, but when you model the aluminum bus, you place the linear loads on the bus and you can do your load combinations.

I answered this question in the Transmission Structure Engineering forum but it seems like I am about the only one that posts there. If you have a copy of ASCE 113, read over the design sections. IEEE 605 also has info on bus design. We are revising ASCE 113 and it should be published in a year or 2. It is tough to get 30 structural engineers from all over the country to agree on anything.

http://www.eng-tips.com/viewthread.cfm?qid=402289

If you are trying to do a full dynamic analysis of the bus support for a short circuit event, you will need the forcing function from the EE's. From what I have seen and done for many years in the business, you use IEEE 605 or ASCE 113 to get the SC loading as a static equivalent load and combine it with the wind or ice load or whatever the substation owner wants you to consider, then design the column and base plate. If all 3 phases are on the same column, the SC forces cancel out on the support beam. The phase spacing on voltages above 345kV is so large, you get individual columns for each phase.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: substation bus structure using STAAD

(OP)
Thank you all for your comments and suggestions. The information provided has been very helpful.

I am also working on base plate design for bus support structures. I am designing moment resisting base plates for HSS square columns. I am having some issues. I am aware of using 0.95 times the depth and width to determine m and n. The issue that I am having is with designing the base plate without it being supported by grout/concrete. The base plate is on leveling nuts. Based on everything I find in AISC design guide examples, all of the base plates are resting on concrete and all of the formulas are based on the base plate resisting on concrete to determine bearing pressure.

Would any one happen to know how to design the base plate without it being supported on concrete? I have designed base plates in the past for other structures in another industry, but all of them rested on concrete/grout. ASCE 113 mentions the design on base plates and the formulas given do not mention concrete strengths.The main issue I am having with the ASCE 113 formulas is the calculation of beff value. My base plate is a square with 4 anchor bolts. The center to center bolt distances are equal. Does AISC have any provisions for base plate that are not supported by concrete? What is the substation industry standard method for designing base plates? See link http://files.engineering.com/getfile.aspx?folder=0... for example sketch. Any suggestions/comments are appreciated.

RE: substation bus structure using STAAD

Yes there are specific guidelines for baseplates without grout, as is common in the electrical industry. My memory is bad but search for Substation Design Guides, or ASCE Design guide 8? Can someone else jog my memory here?

Don't forget the diagonal cuts through the baseplate at the 4 bolt holes in the corners.

RE: substation bus structure using STAAD

Ha, you're absolutely right about the documentation Buggar. We would send binders and binders of finite element output to the client. My pity on anyone who had to decipher that later (especially if they were using another FE software package).

I also recall that ASCE 113 is the right reference for baseplates without grout, but I left my references drive at home today. In short, you'll solve for a force distribution among your bolts using statics, then check the steel baseplate for point loads at bolt locations along straight failure planes (similar to a concrete footing). Often times a 45* failure plane that captures the most heavily loaded bolt (usually based on lateral load at a 45* angle) will govern.

Also, if you're using oversized holes to allow for some anchor bolt placement tolerance (typically a good idea), take that into consideration for distribution of base shear in your bolts. You probably can't count on all of the bolts bearing against the base plate simultaneously unless you tell the contractor to go back and field weld an oversized washer over each bolt. Usually it is easier to just assume the base shear only gets carried by some proportion (half?) of your anchor bolts.

RE: substation bus structure using STAAD

ASCE 113 is the right place to go for the methods. I chair the committee that is revising the guide and we are adding some verbiage about foundations and anchor bolt design. AFA the shear in the bolts, we are assuming the top nut is tightened by the turn of the nut method to make sure the shear transferred to all bolts. The OP has posted the same question in the forum I pointed to above and I have a more extensive answer on how I design bus support base plates there. Lomarandil, you are correct about the FE analysis of plates in bending. You can probably spend several days doing a FEA of a plate worthy of a doctoral dissertation, but structures have been installed and working for many years that were done in the days before computers.

Our industry is somewhat unique in that we are willing to accept some structural failures in the quest for lighter structures. The building and bridge guys OTOH, are not allowed the same latitude. A building collapse or bridge failure is not acceptable under anything other than a 5000 year extreme event. If one of my towers or substation bus structures falls down, you can't charge your smartphone for a few hours or days.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: substation bus structure using STAAD

Exactly. No need to complicate the base plate design -- you'll end up saving the client more by using a quick hand check and a little extra steel than you would by spending hours on an FEA model and getting everything down to a gnat's tooth.

RE: substation bus structure using STAAD

(OP)
Thank you all for your input. It has been really helpful with my task.

@transmissiontowers
I appreciate your information regarding the design of the base plate. Especially the information you posted at thread181-27567 ( http://www.eng-tips.com/viewthread.cfm?qid=402289 ). Do you h--ave any knowledge of designing stiffener plates for base plates? I do not see any info regarding the addition of stiffener plates to the column to help reduce the thickness of the base plate in ASCE 113 and ASCE 48-11. Would you happen to have a design example? Please let me know if you have any recommendations for stiffener added to base plate design.

RE: substation bus structure using STAAD

Stiffener plates can certainly be added but they complicate the simple bending analysis that we use in the hand calculation method. The reduction in thickness (and structure cost) when using them will probably be offset by the increased cost of welding them to the column. You also have to take into account the stiffener punching into your column. The hand method works well enough and is easy to visualize the base plate bending where it welds to the HSS tube. When the complication of the stiffened plate is introduced, you can make some assumptions on the new bending planes but you may be back coding up the base as a FEA to see where the stiffened plate is bending. We have a reference in ASCE 113 to an old book from the Lincoln Arc welding foundation called Design of Welded Structures by Omer W. Blodgett that is very good in explaining base plate and stiffener design. My 1966 edition has a price on the inside cover of $7.00 and you might find it somewhere for a little more but it is a very good reference.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: substation bus structure using STAAD

(OP)
@transmissiontowers
Thank you for your response regarding the stiffener plates. In regards to your method of calculating the bend line for the base plate design, what is your method for determining the tangential bend line length & the distance of the anchor bolt center to the tangential bend line (in ASCE 113 this dimension is designated as ci). I understand the method you used for the parallel bend line. I am trying to determine which bend line (the parallel or the tangential) provides the best base plate design for my hand calculation. Do you subtract subtract the width of the HSS from tangential bend line to account for the galvanizing drain. Please see link for my sketch http://files.engineering.com/getfile.aspx?folder=4... . Here is another document which mentions the tangential bend line http://files.engineering.com/getfile.aspx?folder=0... ,you can see the information much better on this figure when you zoom in (I initially had issues see the words). Here is a copy of ASCE 113 http://files.engineering.com/getfile.aspx?folder=4... . Any recommendations are greatly appreciated.

RE: substation bus structure using STAAD

You will need to check the bending planes that produce the thickest plate so you will check at least 2 in your example sketch and more if you want. The one you call tangential should probably be at 45° to the plate edge to give the shortest bend line. If the tube is square and the 4 bolts are square and the plate is square, the 45° line will be correct. Even if the tube is rectangular and the bolt pattern is also rectangular, the 45° line is the one I check.

Your PLS-POLE reference is more for 8, 12, or 16 sided T-Line poles where they consider bending only along a flat and not tangent to a vertex. Their equations come from ASCE 48-2011.

From ASCE 113 section 6.8 (I wrote some of it about numbers of bolts and the plate thickness, but was talking about big dead end poles with 20 to 48 bolts). Look at Figure 6-1a and check the bend lines 1-1, 2-2, and 3-3. If the hole in the plate is the same size as the HSS tube, you have to subtract the tube width from the effective bend lines 1-1 and 2-2. Choose the maximum bolt load for 3-3 and do the thickness calculation for all bend lines and pick the thickest plate.

There is a paper by a guy named Horn about pole baseplate design that is around 100 pages. Do a search for Daniel Horn and a paper called Technical Manual monopole bases. I found a copy at www.towernx.com that you can download. I believe he was in the telecom world and did large monopole base plates but the concept is the same.

Good luck.

_____________________________________
I have been called "A storehouse of worthless information" many times.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources