what are the white wires for?? thank you!

RE: motor leads i.d.

Temp sensor or switch. Likely an RTD sensor.

Got a close up picture of the label/plate?

Keith Cress
kcress - http://www.flaminsystems.com

RE: motor leads i.d.

(OP)




Thanks

RE: motor leads i.d.

"OVER TEMP PROT 2" on the nameplate may be a clue.
This looks like a single voltage 4 lead motor.

The connection diagram that is not readable in your picture probably says something like:
"Single phase Motor Lead Connections
Connected for Counter - Clockwise Rotation
To Reverse Rotation Interchange Leads $ and %"
Note: "Volts 208/230" on the nameplate refers to the voltage tolerance range, not dual voltages.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: motor leads i.d.

I would agree with you bill on the "Motor Protection 2" and that's why I wanted us to see the nameplate.


helloman22; Use an ohm meter and measure across those two leads.
While you're at it make sure they are not common with any of the big yellow leads at the same time.

Let us know what you get for resistance between those two white leads.

I'd expect for an RTD you'd see something around 110ohms or 1,100ohms. If instead it's a thermistor I'd expect something over 10,000ohms but under 100,000.

Keith Cress
kcress - http://www.flaminsystems.com

RE: motor leads i.d.

Quote (itsmoked)


I would agree with you bill on the "Motor Protection 2" and that's why I wanted us to see the nameplate.


helloman22; Use an ohm meter and measure across those two leads.
While you're at it make sure they are not common with any of the big yellow leads at the same time.

Let us know what you get for resistance between those two white leads.

I'd expect for an RTD you'd see something around 110ohms or 1,100ohms. If instead it's a thermistor I'd expect something over 10,000ohms but under 100,000.
Or I'd get 150 ohms if its a brake coil or a full continuity if it's an NC thermal overload protection switch!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources