PV Inverter - Voltage Rise on One Phase

PV Inverter - Voltage Rise on One Phase

PV Inverter - Voltage Rise on One Phase

(OP)
I'm troubleshooting a PV installation where we have 10 3Ø inverters tied into a single switchboard then running a few hundred feet to the point of interconnection at a dedicated pad mount transformer.

When the PV panel main breaker is off, all voltages are nominal L-G 277V range. When the inverters connect and begin to export, the voltage on phase B & C go up to 280 or so and voltage on Phase A keeps rising up until the inverter shuts off due to overvoltage (around 305V)

I know that voltage rise is to be expected (and conductors were upsized to account for this, the 280V values are in the anticipated range.

But what I cannot figure is the voltage rise on Phase A. My thoughts are that it has to be a cable fault, transformer issue, faulty fuse-link etc. Anything else would effect all 3 phases equally. Right?

RE: PV Inverter - Voltage Rise on One Phase

(OP)
Its rises over time with the increase in power being exported (i.e. when the sun is shining). I cannot figure why it is only on one phase

RE: PV Inverter - Voltage Rise on One Phase

You are going in the right direction. The voltage rise you are seeing is a consequence of Ohm's Law, an there is a difference between phases. Look for lose or high resistance connections in A Phase. It could be that the main breaker is faulty in your panel, you could have a bad termination in the panel or transformer, transformer problem, etc. Work you way back through the system until you don't see the abnormal voltage rise on A Phase or you don't have the PPE to test safely.

I had a similar case a few months back where one of the medium voltage fuses was partially blown. I could measure normal voltage with all equipment off, but when I turned on an inverter B phase voltage rose rapidly. When I plugged in a shop vac, B Phase voltage dropped rapidly.

-JFPE

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources