Punching shear

Punching shear

Punching shear

(OP)
if i have free end cantilever in slab how much length (limit) i will consider in punching area?
i mean limit is d/2 but may be the whole cantilever side will not punch,but what is the limit?

RE: Punching shear

The entire length of cantilever could fail in one way shear.

Punching shear checks only happen at columns (and point loads from above).

RE: Punching shear

Normally basic control perimeter of column is set at 2d

RE: Punching shear

It depends on your local code. Typically a cantilever past a column in excess of 4d-5d will allow you to assume a four sided shear perimeter.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Punching shear

The ACI doesn't address this point. Generally, I consider the edge of the cantilever as a large opening. so I use a distance of 10d. I know that it is conservative but I found no clause in the ACI which details this point.
According to which code it is 4 to 5d KootK ?

RE: Punching shear

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Punching shear

Calculate the perimeter

1 as 4 sided
2 as 3 sided and extending to the ends of the cantilever.

Use the smallest perimeter, or in ACI methodology the one that gives the smaller shear capacity.

RE: Punching shear

And don't forget to factor in the effect that bending has on the shear. The stress is not constant.

RE: Punching shear

(OP)
Thanks guys, really helpfull

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources