Does the IBC base the requirement for standpipe installations on a certain number of stories? I do know that building height and occupancy are factors, but I didn't see anything about the number of stories being a factor.





RE: IBC Standpipe Requirements
The height of the highest story determines whether a standpipe is required. See section 905.3.1 for details (2012 IBC).
Regards,
DB
RE: IBC Standpipe Requirements
Does 905.3.1 answer your question?
http://publicecodes.cyberregs.com/icod/ibc/2009f2c...
Also read 905.3 and 905.3.1 to 905.3.7::
http://publicecodes.cyberregs.com/icod/ibc/2009f2c...