according to NFPA code which i can use for electrical rooms ? FM 200 or CO2
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
fire fighting for electrical rooms
|
RE: fire fighting for electrical rooms
RE: fire fighting for electrical rooms
RE: fire fighting for electrical rooms
8.15.11 Electrical Equipment.
8.15.11.1 Unless the requirements of 8.15.11.3 are met, sprinkler
protection shall be required in electrical equipment rooms.
8.15.11.2 Hoods or shields installed to protect important electrical equipment from sprinkler discharge shall be non- combustible.
8.15.11.3 Sprinklers shall not be required in electrical equipment rooms where all of the following conditions are met:
(1) The room is dedicated to electrical equipment only.
(2) Only dry-type electrical equipment is used.
(3) Equipment is installed in a 2-hour fire-rated enclosure
including protection for penetrations.
(4) No combustible storage is permitted to be stored in the
room.
RE: fire fighting for electrical rooms
Does or will the building have a water fire sprinkler system?
RE: fire fighting for electrical rooms
What kind of electrical room?
Is it a few circuit breaker panels or main power room for entire building?
RE: fire fighting for electrical rooms
cdafd - yes we have water sprinkler system for other factory zones .
the factory comes in 4 floors - in each floor we have electrical room . for lighting - machines --etc
RE: fire fighting for electrical rooms
Under NFPA 2001 the integrity of the enclosure (e.g., Room) requires a "tightness" test as a condition of acceptance and annual tests upon system acceptance. This is required to ensure that the room or space has very limited penetrations or no penetrations. This is done because of the agent cost. FM200 systems are not required to be discharge tested because of the room integrity test.
For CO2 systems, a full discharge test is required. A room integrity test is not required because NFPA 12 establishes minimum leakage rates. However, minimum clearances from energized electrical equipment must be satisfied due because a discharge of liquid CO2 can create a static discharge. See Annex A of NFPA 12.
Depending on the volume of the enclosure, a CO2 system can consume a large amount of space, especially if high-pressure CO2 cylinders are used. FM-200 system will require less space since the agent is more effective at controlling an incipient fire.
You haven't asked anything about the detection systems so I am assuming you have resolved the method for activation of the fire protection system.
RE: fire fighting for electrical rooms
well of course under good HSE practices, you can prevent that but why put something toxic in your building if you can put a safe unit in the beginning and sleep well at nights.