Restricted Earthfault tripping

Restricted Earthfault tripping

Restricted Earthfault tripping

(OP)
please can someone explain why the REF relay on meant to protect a 60MVA 132/33KV transformer will trip whenever a 33kv line feeding from the transformer trips on Earth fault.

RE: Restricted Earthfault tripping

CT polarity or ratio problem.

RE: Restricted Earthfault tripping

What stevenal said.

RE: Restricted Earthfault tripping

Reversed neutral CT.

RE: Restricted Earthfault tripping

Less likely, but it could be due to a blue box if you don't keep up with manufacturer notifications on firmware updates.

RE: Restricted Earthfault tripping

(OP)
Thank you all i am going back to site to look at the polarity, will update u

RE: Restricted Earthfault tripping

CT connection/polarity problem
Usually neutral CT, as ScottyUK said.

of course possible setting mistake.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources