cranked steel bars in ACI 318
hello,
I don't have an experience in cranked steel bars in ACI 318,
could you please refer to the conditions in ACI 318 that define he procedure and limitation ?
Also Why the ACI stop recommend this method?is it because of the earthquake behavior?
RE: cranked steel bars in ACI 318
Back to our main point ,could you refer to ACI procedure for this(Clauses).
See 318-11 11.4.6.5 for the shear contribution.
But the last Closure is 11.4.6.4, besides I am also looking for moment requirement besides shear(where to bend ,how much to bend,etc,)with reference to code requirement .
If you have one of the older CRSI manuals, you can probably find flexural detailing procedures there.
But with alternating live loads on a continuous set of spans the negative moment inflection point extends some distance past the positive moment inflection point.
So it makes it difficult to use the same bar for both positive and negative moments as the bar is needed in two separate locations at the same point along the beam.
In checking older beams for new loads we always have a lack of steel near the upturn in the bar, either positive or negative.
1) is there a standard slope to the sloping portion?
2) would one use normal straight bar extensions past inflection points? Or assume the trussed bars fully developed at the bends? Or as a standard hook development condition at the bends?
3) not all of the reinforcing is hooked typically, correct?
1) No - I've seen many different variations of slope
2) Generally you have two conditions:
I think the trussed bars are developed at the bends - but even with that they occur many times way too soon.
3) The historical practice appears to be that truss bars (bent bars) were used in conjunction with straight bottom bars and much more seldom were straight top bars added.
Quoting from Winter et.al., based on the 1963 Code, "the ACI Code requires only that the inclined part of any such bar make an angle of at least 30 degrees with the longitudinal part". He further stated that they are usually bent at 45 degrees. This was of course a provision for diagonal tension.
I think JAE has described the practice correctly.