13R system what constitutes a non combustible stairwell?

13R system what constitutes a non combustible stairwell?

13R system what constitutes a non combustible stairwell?

(OP)
The architect of record confirmed to me, in writing, that the fire sprinkler system called for is 13R so I'm covered there.

It's your typical four story motel constructed of wood studs plywood wood trusses pretty much what we see every day.

But the stairwells themselves are a little bit different there's wood studs and two layers of 5/8 drywall but the stairs themselves are constructed of concrete and steel nothing combustible.

On past projects I've always sprinklers underneath the landings and inside the stairwells because the stairs were combustible or made of wood.

I am not sure what to do here, my gut feeling is to sprinkle the entire stairway at each floor level and under each landing, but is that required or can I get away with just top of the stairwell and underneath the bottom landing?

RE: 13R system what constitutes a non combustible stairwell?

As far as NFPA 13R is concerned your shaft is noncombustible because the stair are erected from noncombustible materials and the shaftway is constructed where at least 2 layers of fire-resistance rated gypsum wall board erected with staggered joints and fastener placement creates an enclosure of noncombustible materials. The use of wood as a framing material has no bearing on the NFPA 13R sprinkler requirements.

RE: 13R system what constitutes a non combustible stairwell?

(OP)
Thank you Stookey,

Running into this, steel stairs with type III construction, was a new one for me.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources