Weld Reinforcement Height Acceptance

Weld Reinforcement Height Acceptance

Weld Reinforcement Height Acceptance

(OP)
Hi,
Can anyone explain what is acceptance criteria for welding reinforcement? I have actual weld reinforcement which is 20mm but in design it is 18mm. Please give reference also

RE: Weld Reinforcement Height Acceptance

What kind of joint, what shape of weld?

What size of fillet or butt weld, and what diameter (or height and length) and thickness of what material?

(You have asked the equivalent of: "I have an old nut. What will it fit?)

RE: Weld Reinforcement Height Acceptance

Is this question specific for any Code? If so, it would help greatly to share what that Code is...

RE: Weld Reinforcement Height Acceptance

(OP)
It is plate to plate butt joint.size of butt weld mentioned in drawing is 18mm & size of plate is 18mm and material is CS.

RE: Weld Reinforcement Height Acceptance

Right. Now, what Code are you building the pressure vessel in accordance with?
What pressure, what temperature, what service, what fluid?

RE: Weld Reinforcement Height Acceptance

(OP)
its a structural weld . we following AWS D1.1. about 1.5 tons are acting on it.

RE: Weld Reinforcement Height Acceptance

Welcome to Eng-tips. So... how 'bout posting your query in a structural engineering forum where the readers are familiar with structural welding? Perhaps forum725: Welding, Bonding & Fastener engineering.

RE: Weld Reinforcement Height Acceptance

You have full penetration weld in 18 mm plate and the actual thickness of weld is 20 mm. In that case the reinforcement is 2 mm and is acceptable.

RE: Weld Reinforcement Height Acceptance

No, the "distance" measured for a weld reinforcement is from the surface UP to the top (highest point) of the weld bead ABOVE the surface. So, 20 mm weld reinforcement is too high.

Now, the original poster has NOT provided pictures, nor much other information about his structural welds under question. We are ASSUMING he knows how to measure weld reinforcement.

RE: Weld Reinforcement Height Acceptance

Weld reinforcement typically refers to the extra weld material above a butt joint. The typical limit for that is 3mm, so kawishkt is definitely talking about something else.

Perhaps he is talking about a fillet weld? But those are sized by the leg length whereas the reinforcement is above the throat thickness, so I caution kawishkt to make sure he is measuring the right areas.

RE: Weld Reinforcement Height Acceptance

As racookpe1978 stated if your weld thickness is actually 38 mm and the plate thickness is 18 mm, you have too much reinforcement. I am not sure haw one does this, however! And if so the welder should be fired post haste.

RE: Weld Reinforcement Height Acceptance

kawishkt, terminology can be a killer. You should study welding before soliciting advice, particularly in this type of forum.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources