Punching Shear on Concrete Slab
Hi all,
I'm wondering if someone can shine the light on the problem that I am faced with. First, I do want to mention that I am quite new in Concrete Design. So here is my question:
I have a 200 mm thk concrete slab on grade that will be supporting a water tank. The tank has two cradles at each ends and the reaction that I calculated based on the weight of the tank filled with water is 62.5 kN. The contact area of the cradle to the concrete is 0.427 sq.m. I want to check the punching shear as well check flexure to properly design the reinforcement that I need. Could someone lead me to the right path to solve this problem.
The length of the concrete pad is 6430 mm and the the cradles are 4676 mm apart o/c, 877 mm from edge of concrete slab.
The width of concrete is 1766 mm and the cradle length is 1402 mm.
RE: Punching Shear on Concrete Slab
Note, I tried approaching it as a suspended slab supported by concrete column to check for punching shear, but I feel like I'm just lacking some more direction.
Thanks again @KootK
-YoungPadawan
1) Combined footing design.
2) Beam on elastic-ish substrate.
3) Two independent footings with some feel good top steel & concrete between them.
If I analyze it as two separate footings (w/ concrete between them), will I not have the steel reinforcement at the bottom (COMP on top and Tension at the bottom) or T&B (some COMP and TENSION above N.A) and not just top?
I would like to know how one would analyze it as beam on elastic-"ish" substrate, do you have any recommended reading material?
Thanks again!
Two actually independent footings is possible. In which case you wouldn't need all of the concrete between them. I think what KootK is saying is that if you do fill the whole area between them with concrete (for ease of construction / forming), then it would wise to throw in some top steel as well. That's because it will start to mimic a combined footing with negative bending in that portion of concrete that's not really needed. And, the "feel good" steel will help prevent / control cracking.
Personally, I'd just design it as a combined footing.
If you used this approach, you would have only bottom steel required for flexure. That said, I'd throw in a top mat of temperature and shrinkage reinforcement (.0018 Ac) for the reasons that Josh mentioned.
ACI 336.2R-88 Suggested Analysis and Design Procedures for Combined Footings and Mats would be a good place to start. It will be considerable overkill in terms of theory for your situation. Most foundations texts books cover similar territory.
The reasons that I suggested the two independent footing approach are:
1) Based on your loading and proportions, I suspect that a combined footing approach would yield nearly the same answer anyhow.
2) It'll take you ten minutes. I like money.