Hi all

I want to know ventilation required for an ICU , the following screenshot is from the ASHRAE standard . Why is the cfm/ft2 column empty ? does this mean that its designed only on number of people ?

RE: Ventilation for Acceptable Indoor Air Quality

there is always more than basis on which fresh air quantity is determined.

table shows that number of people is generally the most important criteria, if indoor contaminants does not exist, in which case their extraction is primary basis for determining amount of fresh air.

RE: Ventilation for Acceptable Indoor Air Quality

What source are you citing? From ASHRAE 170-13, two OA ACH and 6 ACH are needed.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources