Autotransformer Tertiary Winding?
3

Autotransformer Tertiary Winding?

Autotransformer Tertiary Winding?

(OP)

Friends ,

Why we use tertary winding for autotransformers ? Do we need tertiary winding ?

Thanks,

RE: Autotransformer Tertiary Winding?

Maybe. Is you question about the need for a physical tertiary winding? If so no we don't need a physical winding.

Is your question about the need for a stablizing circuit for zero sequence, or harmonic content? We most likely need this.

Or is your question about the need for a power source for station power? It's got to come from somewhere.

RE: Autotransformer Tertiary Winding?

(OP)
"Is your question about the need for a stablizing circuit for zero sequence, or harmonic content? We most likely need this".


This explanation is what i wanted . Bu i need more detail..I mean how stablizing circuit for zero sequence and harmonic content

RE: Autotransformer Tertiary Winding?

Odd triplen harmonics act like zero sequence currents. The delta provides a trap for zero sequence/triplen harmonics and turns the grounding point into a ground source.

RE: Autotransformer Tertiary Winding?

At present time, in most cases delta winding on (high voltage) autotransformers, as well as YNyn transformers, is not only unnecessary, but also detrimental.
Magnetizing current for large unit is now less than 0.1%, and its zero sequence components are even lower. Furthermore the three-limbs core structure acts as a "phantom" delta tertiary: the high zero sequence reluctance acts as a low impedance path for zero sequence currents; proper design of flux shields allows to cope with umbalanced loads, with are by the way uncommon in high voltage transmission systems.
On the other hand, the delta winding is a weak point from the mechanical point of view, being interested by short circuit currents in case of single-phase to ground fault, which are the most common ones in the HV grid.
Of course, the tertiary winding also increase the cost, weight and losses of the ATR.
Since the '70s we eliminated tertiary delta windind in our YNyn transformers and autotransformers of any size (10 to 600 MVA).
The only (uncommon) case in which you could realy need a delta winding in an HV autotransformer is when you need to substantially reduce the earth fault factor of the transfmission network.
On LV application, you could need the delta winding only if the loads are significantly umbalanced.

Si duri puer ingeni videtur,
preconem facias vel architectum.

RE: Autotransformer Tertiary Winding?

(OP)
FPelec and HamburgerHelper ..Thank you for your help to me ...Those answers are what I need.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources