(OP)
Please see the picture of sleeper supporting pile load over it. The torsion is assumed to be on the pile cap 650x 1000mm.
Minimum reinforcement in ACI has
(Av+2At) = 0.062*(fc^0.5)*bw*s/fyt

bw is the web, for torsion design of pile cap bw should be taken as 650mm, not 1000mm. can anybody clarify with an example.

Link

RE: Torsion design in beams

When it's torsion, you take your smallest dimension since the torsional stresses are equal around the perimeter of the cross section. at least that's how it was explained to me.

RE: Torsion design in beams

(OP)
Hi anybody can give an example of torsion design of beam where breath is greater than depth, as shown in the picture above.
Since some of them still feel that bw is web width = 650 mm as per above figure.

RE: Torsion design in beams

As I said, a beam subjected to pure torsion (or essentially pure torsion when vertical loading is minimal) doesn't care whether it's vertical or horizontal, design procedure is the same for the torsion side of things.

RE: Torsion design in beams

I agree with Jayrod on all counts so far.

As we've discussed previously, however, I feel that strut and tie would be a better choice than sectional methods here based on your proportions.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources