Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
(OP)
Our 69kV underground direct buried cables installation is having a single point bonding system, 3 x 1core-1000MCM cu/XLPE/CuW/Lead/HDPE per phase laid in trefoil formation with associated 1 x 1core - 4/0 cu AWG ground continuity conductor per phase for a span of 2 kilometers, link box with sheath voltage limiter (SVL) is provided at the mid-point of the circuit (1000m). Solidly grounded at both ends.
The cable manufacturer induced voltage calculation at normal condition indicates 0.02 V/m at load current 371 A. During fault conditions we consider 40 kA short circuit fault current. The sheath standing voltage for 3-phase fault is 1.24 V/m which is below our tolerable 5 kVrms, but for single phase to ground fault the manufacturer consider 40 kA fault current and the result is 11.2 V/m that is 11.2 kV at mid-point.
My question: In case of single point bonding system, having 3 cables per phase (trefoil formation), and where system is operated in abnormal condition with only one cable per phase; do we need that the sheath voltage calculation shall take into account the division of any ground fault return current between the three ground continuity conductors?
The cable manufacturer induced voltage calculation at normal condition indicates 0.02 V/m at load current 371 A. During fault conditions we consider 40 kA short circuit fault current. The sheath standing voltage for 3-phase fault is 1.24 V/m which is below our tolerable 5 kVrms, but for single phase to ground fault the manufacturer consider 40 kA fault current and the result is 11.2 V/m that is 11.2 kV at mid-point.
My question: In case of single point bonding system, having 3 cables per phase (trefoil formation), and where system is operated in abnormal condition with only one cable per phase; do we need that the sheath voltage calculation shall take into account the division of any ground fault return current between the three ground continuity conductors?






RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
Thanks
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
"is having a single point bonding system" and also :"Solidly grounded at both ends."
I think you meant the grounding conductor is solidly grounded at both ends.
If all three grounding wires are bonded together at both ends, the return short-circuit current will flow
through all. The current will be shared according to mutual reactance between live, shield and grounding conductors. In my opinion, you may consider the grounding wire as a forth phase.
The mutual reactance it may be k*ln(1/disti,j) where disti,j=the distance between conductor i and j.
For instance between the shield of cable R1[ or A1] from the first group and the grounding wire of the third group Gr3[center-to-center].
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
Thanks for your quick response. You are correct, the ground continuity conductor per phase are bonded together and solidly grounded at both ends. The image you posted is the exact configuration of our cables.
1) We also group bond the metallic shield/sheath of each single conductors in the termination points and connect to the local ground grid via ground wire conductor, is this safe?
2) In case of single conductor (say phase A1) to ground fault within the Phase (A1, B1, C1) of close trefoil formation, what should be the fault current we are going to consider to calculate the induce voltage (sheath voltage gradient) at fault condition; 40kA or 40kA / 3 = 13.33kA?
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
1) In my opinion, using the grounding return wire as shield grounding will add a new voltage drop in the loop so the result could be more than allowable. I should ground the shield directly to a grounding electrode.
2) I think the short-circuit 40 kA it has to be rated per phase. However, the current is shared between parallel cables according to mutual reactance as I said.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
Correct me if I am wrong, for through fault conditions( fault external to the cables) , phase to earth fault , the fault current will be returning through the three of the ground continuity cables and the cable sheath. The fault level in such condition will be 40kA/3.
For any fault within the cable , the cable and the sheath shall withstand 40kA for 1 sec.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
On the other hand, if the cables are arranged as in above sketch, a symmetrical distribution of the currents is expected, indeed. So, in my opinion, each live conductor and grounding conductor will carry 1/3 phase current.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
I just want to understand what’s the difference between the fault external to the cable and within the cable , it is all about the short circuit current value pass through the shield/sheath?
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
In my opinion, one shield -and parallel lead sheath- impedance presents the same impedance as all three grounding wires together. Then the return current will split equally in the shield with sheath and grounding wires-about 20 kA.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
My calculation for positive and negative sequence impedance per kilometer is shown on the link:
https://res.cloudinary.com/engineering-com/image/upload/v1449861373/tips/P_N_Impedance_wqxqjr.pdf
And the zero sequence impedance calculation per kilometer is shown on the link:
https://res.cloudinary.com/engineering-com/image/upload/v1449861522/tips/Z_Impedaance_xz8poz.pdf
Well, I have also noticed that your calculation for impedances of one shield is for 2 kilometer. And that the shields and sheathes are not bonded intentionally together we presume the shield grounded both sides it would be accidentally.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
For copper tape and lead sheath you don’t need skin effect but for grounding wire you do.
The reactance is due to common magnetic flux entering the loop-of the shield and of the grounding
wires.
The copper shield resistance at 70 degrees C [275 mm^2 as per manufacturer catalogue for 40 kA 1 sec.]= 1/58/275*2000*(234.5+70)/(234.5+20)=0.15 ohm
The lead sheath of 0.2 mm thick 60 mm diameter [60*pi*0.2). Rlead=1/4.67/37.7*2000*(1+0.0393*(70-20))=33.68 ohm. Common resistance R1=0.15*33.68/(0.15+33.68)=0.149 ohm.
The loop reactance of shield+sheath and 3 grounding cables is:
X=2*w/10^4*ln(2*av.dist/shield dia)*length[km] w=2*pi*60
av.dist=(dist.A1_Gr2*dist.A 1_Gr3*dist.A1_Gr3)(1/3)=208 mm [measured on sketch- approx.]
X=0.2924 ohm
In this case Zsh=sqrt(0.149^2+0.2924^2)= 0.3277 ohm
Rgr=0.118 ohm [20 oC,skin effect, 3 conductors parallel]
Zgr=sqrt(0.118^2+0.2924^2)=0.3153 ohm.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
https://res.cloudinary.com/engineering-com/image/upload/v1449897633/tips/Induced_Voltage_Calc_at_Normal_Condition_eh64nv.pdf
And at 3-phase fault, phase-to-phase fault, and single conductor to ground fault condition, is shown on the link: With the assumption that the 40000 amps fault current (40kA/3 = 13.33kA) is shared by 3 parallel ground continuity conductor.
https://res.cloudinary.com/engineering-com/image/upload/v1449897648/tips/Induced_Voltage_Calc_at_Fault_Condition_tfrj62.pdf
My question is: Base on your given parameters in your post on 11 Dec 15 21:42, and one shield -and parallel lead sheath- impedance presents the same impedance as all three grounding wires together. Then the return current will split equally in the shield with sheath and grounding wires-about 20 kA, what have you got for induced voltage at fault condition?
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
“The voltage gradient induced in a cable sheath may be considered as a special case in which the conductor that it embraces equal to the mean radius of the sheath. When no other current carrying conductor is in the vicinity, the three sheath voltage gradients for a group of cables in any formation carrying balanced three-phase conductor currents are then given by:” See also:
D2.2 Trefoil Formation Single Circuit. D2.4 Double-Circuit Systems.
Entire Appendix D treats the three phase steady load -or short-circuit case -in which there are balanced three phase currents. You case it is for single phase-to-ground fault.
If you'll treat this as symmetrical components you'll get 1/3 of ground fault current in each phase but this it is not actually-it is a virtual current introduced in order to facilitate the calculation. The actual current flowing through the live faulted conductor it is the entire single phase to ground fault current and no current will flow through the other conductors.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
Current in the grounding conductors will be the result of impedance unbalances between the phases and triplen harmonics.
With a single phase to ground fault the fault current will return via the grounding condustors. This may form a voltage divider with a sheath voltage above ground close to the fault of over half of the phase to ground voltage.
If the source is less than infinite, the sheath voltage will be reduced due to the source voltage drop. (The impedance of the phase conductors is less than the impedance of the grounding conductors.)
However, the actual sheath voltage above ground in the event of a single phase to ground fault may be many times the calculated voltage due to induction.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
Your statement is actually found in IEEE Std 575-2014 para E.1.3.3 single-phase ground fault (solidly grounded neutral) which states that "Precise calculation of shield/sheath overvoltages for underground-fault conditions requires a knowledge of the proportion of the return current that flows in the ground itself and the proportion that returns by way of the parallel GCC. This depends on a number of factors, which are not usually accurately known. Fortunately, however, the overvoltages of practical interest are those between shields/sheaths and the parallel GCC, and these can be simply calculated by the assumption that this conductor carries the whole of the return current. This assumption is normally accurate and leads to shield/sheath overvoltages that are slightly higher than those observed in practice."
Per 7anoter4 point of view, if all three grounding wires are bonded together at both ends, the return short-circuit current will flow through all. The current will be shared according to mutual reactance between single conductor, shield/sheath and grounding conductors.
Do we have mathematical representations to demonstrate the return fault current are actually not equally divided between live conductor shield/sheath, and ground continuity conductor during a single conductor to ground fault?
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
An I2R drop from a voltage divider circuit is entirely different.
With a single phase to ground fault where the current is returning through the ground conductor results in a large I2R drop in the ground conductors.
If you concentrate on the induced voltage and ignore the I2R voltage resulting from the ground current in the grounding conductor you may someday be facing a due diligence issue in front of a coroner's jury.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
- For the ampacity, the total load for each phase shall be 1112 A and each 1core x 1000MCM will carry 371 Amps since the phase contains three cables in trefoil formation. The source is a 3-winding autotransformer; rated at 133 MVA 69kV secondary, solidly grounded neutral; feeding 69kV gas insulated switchgear (GIS). Applying derating factors, the lowest calculated single conductor ampacity is 444 Amps, still higher than the anticipated 371 Amps.
- Each cross section of single conductor CuW shield / lead sheath in case of short circuit is capable to withstand 40 kA for 1 second.
- Each 4/0 AWG ground continuity conductor is calculated to carry 40 kA. We have 1 GCC per phase. Total 3 parallel GCC.
So, I am more concern with the induced sheath voltage at fault condition; single conductor to ground fault, to my opinion poses safety issues with the selected type of single end (point) bonding at mid point within a span of 2 kilometer as mentioned in my first post.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
Case 1.Conductor phase-to-ground fault cable outside. All shields and sheaths grounded in the middle only. The short-circuit current returns through grounding wires and earth.
Case 2.Conductor phase-to-ground fault inside one cable. Short-circuit current returns to source through this cable shield also.
Case 3.Conductor phase-to-ground fault cable outside. Cable shields grounded both sides.
Case 4. Other possible case.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
- Maybe, because the conductor currents tend to induce currents in parallel metallic paths – including the cable sheath?
- Allowing these sheath currents to flow generates losses that can reduce ampacity 30-40%
7anoter4, the Case 1 and Case 2 are more applicable to our cable configuration. However, could you please explain the difference of fault outside and inside the cable;
- Case 1. Conductor phase-to-ground fault cable outside
- Case 2. Conductor phase-to-ground fault inside one cable
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
Case 1.
The short circuit point is located in the supplied equipment-or installation.
"the fault external to the cable".
The short-circuit current flows in all 3 parallel live cables of the faulted phase.
Shields grounded at middle distance only.
No current flows in the shields.
The short-circuit current flows in all 3 parallel grounding cables.
Case 2.
when one cable- of three per phase- insulation breaks down in one point and the sheath or shield will be grounded in one more point-that means inside the cable.
The short-circuit current flows in a part of the shield up to the grounding connection point- only in the faulted cable.
Case 3.
The short circuit point is located in the supplied equipment-or installation.
"the fault external to the cable".
The short-circuit current flows in all 3 parallel live cables of the faulted phase.
Shields grounded at both ends.
The return short-circuit current flows through all 18 shields in parallel with the 3 grounding conductors.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
The return short-circuit current flows through all 9 copper tape shields and 9 lead sheaths in parallel with the 3 grounding conductors.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
The IEEE-575 does an excellent guide for bonding the sheath of HV cable, and it does mentioned the safe limit for induced sheath voltage at normal condition as 65 Volts. But at fault condition, the IEEE-575 didn't recommend any safe limit value of induced sheath voltage e.g. 1000 Volts, 5000 Volts etc. at fault condition, any idea?
I've found one thread below discussing similar topic but can't find standard acceptable value of induced sheath voltage at fault condition. Thanks.
thread238-399727: Problem: High cable sheath current for 34.5kV distribution systemLink
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
http://www.akpowersolutions.com/Media/Products/AKP...
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
During a Ø-grd fault, there will be current in only the faulted phase, the earth, and the ground continuity conductors. The level of current in the phase is not 1/3 of the maximum design current, but is dependent on the source and cable positive- and zero-sequence impedance. There will be voltage induced in the shield from the phase current. There will also be a ground potential rise at the mid-point because of currents in the earth and ground continuity conductors. The total voltage between the shield and ground at the middle depends on both the shield induced voltage and the ground potential rise. Calculation will be complex. Perhaps a program such as SEL MALZ and SPLITS could be used. See http://www.sestech.com/Products/SoftModule/Splits....
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable
But I want to find out when you mentioned that during phase to ground fault, e.g. single conductor to ground fault (trefoil formation), the level of current in the phase is not 1/3 of the maximum design current (40kA), but is dependent on the source and cable positive- and zero-sequence impedance.
In my understanding, during phase to ground fault, each cable within the phase (say phase A) of trefoil formation, the current through each cable will be 40kA/3, assuming equal impedance due to the source is a 3 winding auto XFR, the tertiary winding will act as balancer for short circuit current flowing back to the source.
RE: Sheath Standing Voltage at Fault Condition of HV 69kV cu / XLPE Cable