B31.3 Fitting Hydrotest
I am designing a fitting to B31.3 that is a cored bar material NPT threaded on both ends with a 1/4" bleed in the middle of it. Is a hydrotest still required if no welding is performed? I think it does, but couldn't find anything in the Code that says one way or the other. Thanks!
RE: B31.3 Fitting Hydrotest
Sometimes its possible to do all the right things and still get bad results
Sounds like a strange bit of pipe to me so test it as part of the system test.
a drawing, photo or sketch might help, but if it can see pressurized fluid then it's part of the system.
345.1 says" Prior to initial operation, and after completion of the
applicable examinations required by para. 341, each piping
system shall be tested to ensure tightness. The test
shall be a hydrostatic leak test in accordance with
para. 345.4 except as provided herein."
The fitting is owned by a services company and wouldn't be hydrotested with the original piping system since it will get moved from site to site. I suppose it would be considered its own "system" in that case.
Just imagine what would happen if it failed in service?
Interpretation: 20-24
Subject: ASME B31.3-1998 Addenda to 1996 Edition, and B31.3-2002 Edition, Para. 345.2.3, Piping Subassemblies
Date Issued: May 20, 2005
File: B31-oS-1S7 and B31-oS-319
Question (1): Does ASME B31.3-2002 Edition define "subassemblies" the same way as it defines "piping components"?
Reply (1): No.
Question (2): In accordance with ASME B31.3c-1998 Addenda and ASME B31.3-2002 Edition, does para. 34S.2.3(a) allow piping components to be independently tested as required by para. 345.1, and then assembled and placed into service with no additional leak testing?
Reply (2): No, unless the system is assembled with flanged joints or closure welds as described in paras. 34S.2.3(b) and (c).
Hope that helps,
DD
DekDee, That interpretation makes it sound like we won't be able to install a threaded fitting onto a piping system after the system hydrotest. It sounds like threaded instrumentation gauges would also not be allowed to be installed post-system hydro since they aren't closure welds or flanged connections...
If repairs or additions are made following the leak test, the
affected piping shall be retested, except that for minor
repairs or additions the owner may waive retest requirements
when precautionary measures are taken to assure
sound construction.
So you need to convince the Owner that sufficient "precautionary measures" are taken, one of which is almost certainly that the particular item has itself been pressure tested to a pressure at least similar or higher than the piping system to which it is becoming attached to, even if for a short time.
I hate the word "temporary" when it comes to anything to do with pressurized systems as the implication is that testing, operation and systems can somehow be magically reduced compared to "permanent" piping for no particular reason.
Many many failures have occurred on "temporary" connections, especially where this operation is undertaken infrequently or by inexperienced or inadequately trained operators and supervisors.
Of course frequent make / break connections are also much more at risk of incorrect assembly, no or inadequate testing which then fail in practice.
LittleInch, considering this as a minor addition is probably the way to go. My client has Job Risk Assessments and Installation Procedures for this task in place already so we should have the sound construction portion covered. Doing a leak test of that threaded connection is complete overkill if the original system and our fitting were tested independently. Thanks for your help!