Pressure Test For Chilled Water System
Pressure Test For Chilled Water System
(OP)
Hi i am working as HVAC engineer i want to now what the Value of Operation Pressure for Chilled water system and Recommended Pressure Test for chilled water pipe System





RE: Pressure Test For Chilled Water System
in you title test pressure is mentioned, but here you are talking about operating pressure. which one concerns you.
RE: Pressure Test For Chilled Water System
Test pressure is usually 1.5 times the design pressure or max operating.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Pressure Test For Chilled Water System
Operation Pressure as your Reply 3-4 bar in close Loop it mean the test Pressure if 2 times from this Pressure it safe
RE: Pressure Test For Chilled Water System
RE: Pressure Test For Chilled Water System
RE: Pressure Test For Chilled Water System
10 bar can be working pressure for water supply or fire extinguishing systems, and than 15 bar can be testing pressure, but not for circulating systems.
can you give us some example of equipment - fan coils, heat exchangers or similar attached to your chilled water loop?