PLC5 & Poweflex 700 RIO Comm issue

PLC5 & Poweflex 700 RIO Comm issue

(OP)
I am working with a PLC5 and a Powerflex 700 and my personal PC.
I want to connect the PLC5 and the Powerflex 700 trough RIO (Remote I/O). I already setup the Rack Address, Group, Rack Size, Baud Rate in my devices and the LED indicators are green. But I dont know how to Configure RSlogix in order to send and receive information from the PowerFlex 700. I basically want to start the drive and stop the drive, and receive basic infromation like motor speed.

I am using:
PLC 5/40 Channel 1B Scanner mode
PowerFlex 700 Variable Frequency Drive with 20-COMM-R adapter.
3 Pin Cable to communicate trough RIO.
Personal Computer to PLC5 trough DH+ To USB.
RsLogix 5

RE: PLC5 & Poweflex 700 RIO Comm issue

If you can get it to communicate, you will need to use message files to send and receive data to/from the drive. I'm not familiar with the 20-comm-R card, I've used the 20-comm-E and 22-comm-E. Those cards probably work the same way. You will need to look at the manual for that card and figure out what registers are used for status/commands/data. I think it would be easier to use modbus RTU on something that old.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close