Water well clearance from diesel genrator

Water well clearance from diesel genrator

(OP)
Hello,

Thank you in advance fro your time.

This is case in Federal land of Canada, We have water wells supplying water to Town for few decades. As part of disaster mitigation funding we are proposing to installed Diesel genset to supply power in emergency situations to water wells.
Federal regulation do not have clear indication of how far diesel tank shall be located form drinking water wells. Now we have been asked to comply with provincial guideline which has clear instruction on distance between water week and diesel tank. AS per provincial regulation distance between water well and diesel source shall be minimum 100 mt.

Could you please share your experience on clearance requirements between water well and diesel gneset.

Thanks,

RE: Water well clearance from diesel genrator

You must be misreading. Standby units are installed with secondary containment tanks for diesel fuel. Tanks are usually above grade. Have never had an issue with separation distances.

RE: Water well clearance from diesel genrator

(OP)
Hi Bimr,

Yes. We do have double wall tank for diesel tank. Owner forcing us Water Act which say 100m clearance require. However it do not specify distance with double wall tank.

That's why I asked question to forum to get more information from real scenario and solution to that.

Regards,


Below text copied from Province of Alberta " Water Act"
-----------------------------------------------
Distance from sources of contamination
46(1) No person shall locate or drill a water well for the diversion
of groundwater, other than saline groundwater, closer to a thing
described in Column 1 of Table 1 than the distance specified in
Column 2 of Table 1.
(2) If the diversion of water from a water well is licensed for
municipal purposes, no person shall locate or drill the water well
closer than 100 metres from any thing listed in Column 1 of
Table 1
Table 1
Column 1
Sources of Substance
Column 2
Minimum Distance
Required
Watertight septic tank or sewage
holding tanks
10 metres
Sub-surface weeping tile effluent
disposal field or an evaporation mound
15 metres
Sewage effluent discharge to the
ground surface
50 metres
Section 47 AR 205/98
WATER (MINISTERIAL) REGULATION
33
Sewage lagoon 100 metres
Above ground storage tanks containing
petroleum substances
50 metres

RE: Water well clearance from diesel genrator

Unless there is more than what you posted, the paragraph does not state that a standby generator with diesel storage tank shall not be located near a well.

It states that you shall not locate or drill a water well for ... presumably from an existing Above ground storage tanks containing petroleum substances.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close