Wstinghouse HU Xfmr Diff Relay

Wstinghouse HU Xfmr Diff Relay

Wstinghouse HU Xfmr Diff Relay

(OP)
I guess I've been out of the field too long.

does anybody remember the Westinghouse IL for their HU relay?

old field guy

RE: Wstinghouse HU Xfmr Diff Relay

Have the papers but never tested one though.

RE: Wstinghouse HU Xfmr Diff Relay

(OP)
Thanks for the links, folks.

A friend is working on some 'legacy', i.e., "older than dirt" equipment. He was specifically asking if the Westinghourse HU had a functionality similar to the GE BDD, where one can measure unbalance current on Terminals 8 and 9 to validate the proper setup of the unit.

Neither he nor I see that functionality in the HU.

It's been quite a while since I got to play with these things. My old service 'library' has disappeared, along with a good portion of my memory of this fine equipment.

old field guy

RE: Wstinghouse HU Xfmr Diff Relay

I'm not sure if this is what you are looking for, but as an in-service test he can measure the voltage across the 'operating circuit resistor' at the top of the relay and compare it to figure 16 on page 32 IL 41-347.1S

https://library.e.abb.com/public/7609d5d6fbd3387ec...

RE: Wstinghouse HU Xfmr Diff Relay

(OP)
JG-

Yes, that will work. It's just that the GE relay has that function brought out to a couple of easily accessible terminals on the case.

old field guy

RE: Wstinghouse HU Xfmr Diff Relay

It is the big resistor at the top, so the two wired terminals should be pretty easy to clip on to.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources