Why sometimes current supervision is selected when using undervoltage protection ?
Thanks for replying.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Undervoltage Protection with Current Supervision ?
|
Undervoltage Protection with Current Supervision ?Undervoltage Protection with Current Supervision ?(OP)
Why sometimes current supervision is selected when using undervoltage protection ? Thanks for replying. Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesThe world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
Engineering-centric businesses face a number of challenges today, but unmanageable design and change processes don’t need to be counted among them. Download Now
|
RE: Undervoltage Protection with Current Supervision ?
RE: Undervoltage Protection with Current Supervision ?
Canadian Electrical Code.
Undervoltage protection
28-400 Undervoltage protection required for motors (see Appendix B)
Motors shall be disconnected from the source of supply in case of undervoltage by one of the following means,
unless it is evident that no hazard will be incurred through lack of such disconnection:
(a) when automatic restarting is liable to create a hazard, the motor control device shall provide low-voltage
protection; or
(b) when it is necessary or desirable that a motor stop on failure or reduction of voltage and automatically
restart on return of voltage, the motor control device shall provide low-voltage release.
Current supervision.
This is often used to prove that a motor is running. This feature is often found in refrigeration control circuits.
Current above threshold is good. Current below threshold alarms.
Bill
--------------------
"Why not the best?"
Jimmy Carter