Hi All,
I am designing cross bracing consisting of stocky tubes say 10x10. They have been analyzed as compression and tension braces. When they are subjected to lateral loads, one brace will be in tension and the other in compression. In such scenario, it can be assumed that the tension member braces the compression member in and out-of plane direction. That is for the compression member half the unbraced length can be used to calculate the compression capacity.
Lets consider a scenario where both braces are in compression (one brace experiencing high compressive force and the other one a smaller force), say under gravity loads. Both the braces have similar length and similar cross sectional properties. In this case, I was in the impression that the braces need to be designed based on full length of the member. But, I was told that, even when both the members are in compression, it can be assumed that they brace each other in in-plane and out-of plane directions. This is because, when the brace with higher compressive load starts to buckle, the one with the smaller force goes into tension. Is it correct to assume the half the unbarced length for the design in such circumstances?
I am designing cross bracing consisting of stocky tubes say 10x10. They have been analyzed as compression and tension braces. When they are subjected to lateral loads, one brace will be in tension and the other in compression. In such scenario, it can be assumed that the tension member braces the compression member in and out-of plane direction. That is for the compression member half the unbraced length can be used to calculate the compression capacity.
Lets consider a scenario where both braces are in compression (one brace experiencing high compressive force and the other one a smaller force), say under gravity loads. Both the braces have similar length and similar cross sectional properties. In this case, I was in the impression that the braces need to be designed based on full length of the member. But, I was told that, even when both the members are in compression, it can be assumed that they brace each other in in-plane and out-of plane directions. This is because, when the brace with higher compressive load starts to buckle, the one with the smaller force goes into tension. Is it correct to assume the half the unbarced length for the design in such circumstances?






RE: Effective Length of cross braces
I don't know what you're designing, but If it's anything like the towers that we design where I work, it's hard to imagine a controlling load combination in which both braces would be in compression.
RE: Effective Length of cross braces
I completely agree with you. I case of tower design, under all loading conditions, whether gravity combinations or lateral combinations, the braces will be in compression and tension. I am talking about horizontal lacing in industrial buildings comprising of trusses.
RE: Effective Length of cross braces
thread507-396523: The effective length of strut in a X- Bracing
Also these:
thread726-120298: Unbraced length of X-brace design
thread507-258454: x-bracing design considerations
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: Effective Length of cross braces
Could you please elaborate on the situation a bit more? What is the actual physical length of the tubes? What are the members are you lacing together? It sounds like you're talking about horizontal trusses with cross-braced panels, but I'm not entirely sure. Given the size of the members you're worried about effective length for, I suspect you might be talking about bracing for roof trusses or something. A sketch would be nice.
Really, it kind of sounds like you're giving a garbled description of the tension-only member assumption for cross-bracing. Just to make sure, you aren't either:
1. misunderstanding the concept of tension-only cross-bracing or
2. getting an explanation of why cross-bracing is often slender for compression from another engineer who might be misunderstanding it,
...are you? You say you're assuming they can take compression, but the wording of your last sentence... I don't know.
RE: Effective Length of cross braces
Ah, so allowance can be made if they're connected. I definitely like the idea of using the ~0.7 values rather than 0.5.
RE: Effective Length of cross braces
Yes, members are physically connected at the midpoint. They are connected using the knife plate detail.
The length of the tubes is around 30’. The members that are laced together are HSS10x10x8 tubes.
Attached is the sketch. Correct, I am talking about bracing at the roof (diaphragm). These are not tension only bracing. We have developed a 3D model for the analysis. We see compression forces in both the braces under gravity loading scenario in the top chord level. I don’t know how true this behavior is. In these cases, we have assumed that the unbraced length of the members is half the full length for the design.