wood framed shear walls - sheathing panels applied vertically

wood framed shear walls - sheathing panels applied vertically

(OP)
Do the values in the 2008 SDPWS Table 4.3A Nominal Unit Shear Capacities for Wood-Frame Shear Walls vary if your sheathing runs vertically instead of horizontally? The shear walls I am considering are framed at 24"o.c. and sheathing is spec'd as 15/32 APA Rated Sheathing. I haven't found any information indicating a required sheathing direction associated with the shear values given in Table 4.3A.

Thanks

RE: wood framed shear walls - sheathing panels applied vertically

I can't comment on the SDPWS however the Canadian code has no problem with this provided the horizontal joints are staggered.

RE: wood framed shear walls - sheathing panels applied vertically

And blocked. Vertical application is normally how it is done here. 2thumbsup

However, for GSB and GWB, horizontal is normal.

Mike McCann, PE, SE (WA)


RE: wood framed shear walls - sheathing panels applied vertically

(OP)
msquared48 - vertical application makes a lot of sense, (in this case they are interested in reducing the amount of blocking and thus thermal bridging), but yes the walls are calling for blocking.

Is there any code requirement for the panels to be staggered when applied vertically? Thanks!!

RE: wood framed shear walls - sheathing panels applied vertically

For double sided shear walls, yes. I believe it is one of the notes on the shear wall tables in the IBC.

Mike McCann, PE, SE (WA)


RE: wood framed shear walls - sheathing panels applied vertically

We have modification factors for unblocked shear walls. In fact, generally, the unblocked capacities are more than adequate for walls with low unit shears.

RE: wood framed shear walls - sheathing panels applied vertically

(OP)
MSQUARED48 - Thanks again. You are correct - per the footnotes in the SDPWS T4.3A footnote 6 calls for staggered panel joints when nail spacing is less than 6" o.c. and panels are applied to both sides of the wall. Otherwise, as I now understand it, panels are not required to be staggered.

Thank you.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close