Petroleum resistant concrete
I'm about to place concrete for helicopter parking pads. All was well until the client pointed out that the existing concrete directly under the copters was scaling off due to the petroleum by products (hydraulic oil, fuels, lubricants...) leaking from the copters. He wants to make sure this doesn't happen to my concrete. Anybody have any suggestions to making concrete resistant to petroleum?
RE: Petroleum resistant concrete
Usually all parking and maneuvering areas of the airfield are concrete. This is for two reasons the first is strength. Asphalt will soften in hot weather and the tires or skids will sink into the surface. The other is that hydrocarbons will dissolve asphalt but not concrete.
Are you sure that the spalling is due to the petroleum and not some other cause like freeze thaw? Or some other chemical? You might want to have some cores tested to determine the cause of the deterioration. (have the lab check for air entrainment as well. If there is no air in the original mix this could be the cause of the problem.)
Where is this located? If you are in a location where freeze thaw is not usually a problem then air might not have been used in the original mix.
The DND Pavement Maintenance Manual (Department of National Defense, Canada’s equivalent to the US DOD) makes no mention of hydrocarbon attack of concrete.
The Canadian concrete code (CSA A23.1 para 15.8 ) calls for “Concrete exposed to heavy concentrations of light mineral oils, industrial chemicals, or trade wastes shall be given a protective coating..” There is a note that refers to PCA bulletin Effects of Substances on Concrete and Guide to Protective Treatments. 1S00I.07T, 1989. It might have some guidance that could help you.
I would always use sulphate resistant concrete when in contact with ground. I’d suggest that as a minimum you use 32 MPAa maximum water cement ratio 0.45 and entrained air of 6 to 9 % for max 10 mm aggregate, 5 to 8% for 14-20 mm aggregate and 4 to 7 % for 28-40 mm aggregate. (These values are right out of CSA A23.1)
If there is oil contamination on the existing concrete this should be removed by either steam or chemical cleaning or removal of the contaminated concrete depending on extent of contamination or the overlay will not bond to the existing layer.
Also pay particular attention to the curing of the concrete. This will increase resistance to all types of chemical attacks as well as freeze thaw.
Rick Kitson MBA P.Eng
Construction Project Management
From conception to completion
www.kitsonengineering.com
I think that RDK gave a great comprehensive note. Keep up good work!
Best regards.
You mention the desert of Arizona. This could be a clue when mixed with the petroleum. If your aggregates are porous, or if your concrete matrix was a bit porous near the surface, then petroleum products penetrating into the matrix can then be heated by the sun on the concrete and the resulting vapor pressure increase, particularly at the aggregate interface level where the tensile bond is less than the matrix tensile strength, can cause "flaking" or minor spalling. Keep in mind that this process can also be "fatigue" oriented in that multiple times of building vapor pressure will ultimately fail the concrete on a "sub-macro" level (not really microscopic, but not larger spalls either). Couple this with the abrasion/localized impact of the landings and you could easily rationalize your result.
How to fix? Dense, high quality concrete, 4000 psi or higher. Use dense aggregates with low absorption capability. You could consider using a hardtopping or coating, but I think good dense concrete with a hard trowelled surface and wet curing for at least 14 days will give good service in this application. If you need to reduce the "slipperness" of a hard trowelled finish then roughen it after curing with abrasive wheels or brushes, but get the hard trowelling done first.