Connecting Angle to Beam/Joist with C-Clamp

Connecting Angle to Beam/Joist with C-Clamp

Connecting Angle to Beam/Joist with C-Clamp

(OP)
Hello, long time lurker and this is my first post. During a walkthrough of a new building nearing completion, I noticed the supports for an HVAC unit (2 angles) were connected to the flange of an I-beam and a steel joist with beam clamps (C-clamp?). It is my understanding that these are used to attach equipment to the flange of supporting members, but the contractor thinks they can be used to connect steel elements (as opposed to welding/bolting).


Is there anywhere in IBC or AISC that specifically addresses this? It seems common sense to me, but apparently not others.

RE: Connecting Angle to Beam/Joist with C-Clamp

Clearly, a clamp can be used to connect two steel members. They've done it. Of course, whether or not that's a good idea is another matter. If this were my baby, I'd be crying foul as follows:

1) Clamps might come off as a result of vibration or folks messing with them.

2) When clamps come off, the mechanical unit could squash some poor bastard.

3) KootK not comfy with the implied liability. Perhaps Joe Builder would be willing to take it on?

4) No? Too bad, so sad.



I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Connecting Angle to Beam/Joist with C-Clamp

They're used all the time for temporary falsework (and the California Falsework Manual has some guidance if you become inclined to justify it), but I agree with the reservations noted for permanent applications.

The largest risk in my mind is that vibrations loosen the screw over time.

RE: Connecting Angle to Beam/Joist with C-Clamp

I don't have a problem with beam clamps in light duty applications, but I do have a problem with that kind of beam clamp. There's nothing keeping it from slipping out.

I'd want something more along the lines of these:

http://www.beamclamp.com/connection-solutions/cate...

RE: Connecting Angle to Beam/Joist with C-Clamp

(OP)
My thoughts exactly. There's nothing to prevent this thing from shaking loose over time. It's in a bus maintenance facility too, there will constantly be people walking around underneath.

Ultimately, we have to provide our own CO, so I'll just say no until they fix it.

RE: Connecting Angle to Beam/Joist with C-Clamp

Do the contract documents detail a connection? Even a contractor with half a brain knows clamps aren't a permanent connection. I've seen contractors play dumb in the hope of an extra.

RE: Connecting Angle to Beam/Joist with C-Clamp

I like it when they use clamps on light gage purlins and fold the stiffening lip down flat.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources