Steam pressure vs temperature
Gents,
a heat exchanger is to be supplied with steam at 147 psig and (363F) from higher steam source @429 psig& 456 F through pressure control valve,
my question what will be practically the temperature downstream the pressure control valve, since there's no heat exchange? is it as per the steam table 147 psig correspond to 363F.
RE: Steam pressure vs temperature
No, it is pretty close to the source temp of 456F. You might get some JT cooling, but this is a pretty small dP. The LP steam will be superheated, not saturated so the saturated steam table doesn't have much relevance.
David Simpson, PE
MuleShoe Engineering
In questions of science, the authority of a thousand is not worth the humble reasoning of a single individual. Galileo Galilei, Italian Physicist
Estimate this to be at 405degF downstream of the PCV at 147psig (still superheated), so you have to desuperheat another 42degF to reach saturation temp of 363degF.
What kind of solution to desuperheat the steam and achieve 363 F.
Regards.
Here is a sample vendor offering desuperheater nozzles - there are some others also which you can find on the net.
http://www.spiraxsarco.com/Documents/Desuperheatin...
You may wish to buy the desuperheater nozzle only from this vendor and fix up the PCV and TCV and piping yourself if that suits you.
Thanks a lot georgeverghese