Ulitmate load to use for Anchor bolt check ACI - Ap. D

Ulitmate load to use for Anchor bolt check ACI - Ap. D

Ulitmate load to use for Anchor bolt check ACI - Ap. D

(OP)
I have 25k uplift and 9.5k shear loas based on allowable strees method.
To check Appendix D ACI. I need to convert these to Ultimate loads (Nua and Vua), may I ask what above number has to be multiplied to so I can get correct value for Nua and Vua?

Thank you

RE: Ulitmate load to use for Anchor bolt check ACI - Ap. D

Where do the uplift and shear come from? EQ, DL, LL, WL? You would use the LRFD load combinations in ASCE 7-10 2.3.2 or ACI 318 chapter 9.

RE: Ulitmate load to use for Anchor bolt check ACI - Ap. D

(OP)
sandman21 (Structural,
These are the values I got from the drawings of a structure built 1954.
There was no break out of the numbers to tell me how much of it was what kind of load.
My assumption is the Uplift is due to wind load as well as shear.
So what will be the multipliers?

Is it wrong that I multiply Uplift by 0.9 and Shear by 0.85?(Vu=0.85Vn and Tu=0.9Tn)

Sorry my knowldge in this area is bit rusty. I appreciate the direction.

Thank you

RE: Ulitmate load to use for Anchor bolt check ACI - Ap. D

I typically use the ultimate load factor of 1.45 to convert ASD to LRFD.

RE: Ulitmate load to use for Anchor bolt check ACI - Ap. D

Allowable loads for wind are, Deadload + .6Wind Load. So to take the loads from allowable to ultimate would be 1/.6= 1.67 or 1.6. So your Tu=1.6*25k and Vu=1.6*9.5k. If you are looking for the phi factors they are applied to the Vn and Tn.

RE: Ulitmate load to use for Anchor bolt check ACI - Ap. D

(OP)
sandman21 (Structural), I thought Tn and Vn are the ASD loads but thibking more I am feeling they are the factored loads
so am I right the Tn and Vn are factored loads?
So there is difference between factor load and ultimate load?

RE: Ulitmate load to use for Anchor bolt check ACI - Ap. D

Tn and Vn are the tension and shear CAPACITIES or strength in tension and shear. You do not factor those up, but rather down with phi factors.

Loads are factored up from service levels - for your unknown mix of dead, live, wind, etc. I'd use 1.5 to 1.6.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Ulitmate load to use for Anchor bolt check ACI - Ap. D

I tried to tell them this would happen if we left ASD.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources