Substation Installation Choices

Substation Installation Choices

Substation Installation Choices

(OP)
What are the advantages/disadvantages/potential problems that need to be addressed when choosing between the following installations?  Cost and redundancy need not be addressed.

The installation of a single 4000kVA transformer or two 2000kVA transformers.

RE: Substation Installation Choices

jlazucena

4000kva advantages
only one main breaker high side
only one main breaker low side
only one set of relays
only one SWGR
no problem about getting load balanced
no problem about getting one XFMR overloaded while the other has spare capacity

2x2000 advantages
smaller short circuit current in the secondary

If a capacitor bank is considered and you have some VFD (harmonic production)you can put most of these VFD in one XFMR and have the other XFMR a rather clean


RE: Substation Installation Choices

As mentioned by jlazucena these items translate to initial equipment cost and a larger substation space.  However two units mean that you have operational flexibility.

RE: Substation Installation Choices

Suggestion: Beside what was mentioned in the first reply post, there is a need for more info regarding those two 2000kVA transformers, namely, how they will supply load, whether they will have their secondary in parallel, etc. Please, elaborate.

RE: Substation Installation Choices

Dual Trfs. allow offers the ability to automatically roll load to an alternate power source source within just a few cycles versus waiting for field repairs.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources