The effective length of strut in a X- Bracing

The effective length of strut in a X- Bracing

The effective length of strut in a X- Bracing

(OP)
Hi,
In a X-brace , is it possible to take advantage of tension member countering the buckling of compression member ?
In that case is thee any literature or paper wherein this is quantified in numerical terms.
Thanks

RE: The effective length of strut in a X- Bracing

And sometimes not depending on how much tension is in the other brace...the paper may discuss this but I've read many articles that suggest it isn't the case where it ALWAYS works or always doesn't.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: The effective length of strut in a X- Bracing

I believe that the design standard for latticed transmission towers gives some middle of the road, easy to apply guidance on this.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: The effective length of strut in a X- Bracing

For laced members, I've seen the compression leg (lace?) allowed K=0.7 to account for a tension member connected at midspan.

RE: The effective length of strut in a X- Bracing

Recent research also shows that you probably can't take a reduced K factor when members are in the post-elastic range (such as special concentric braced frames).

RE: The effective length of strut in a X- Bracing

(OP)
Hi Lomarandil,
Am I correct in assuming that K is applicable to the full diagonal rather than half the diagonal.
For e.g if the brace frame is 10 x 10 square then effective length will be 0.7 x diagonal = 0.7 x sqrt(2)*10 = .7 x 1.42 x 10

RE: The effective length of strut in a X- Bracing

This topic was addressed in a 2013 (3rd quarter) Engineering Journal paper ("Stability Design of Cross-Bracing Systems for Frames") by Eric Lui and Xiaoran Zhang. The paper is available (free of charge to AISC members) on the AISC website at www.aisc.org. The paper concludes with an easy-to-follow, 6-step design procedure.

RE: The effective length of strut in a X- Bracing

Angre -- correct, applied to the full length of the diagonal.

RE: The effective length of strut in a X- Bracing

One other thing to consider (and Hokie93 - I'm not sure if the paper covers this or not) - is that a typical X-brace bay may produce compression in both braces from dead loads and other vertical loads, that when combined with lateral wind or seismic result in your tension brace having less tension in it and your compression brace having more compression in it than a more simply lateral hand analysis might show.

This has the effect of reducing the lateral bracing ability of the tension brace on the compression brace.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: The effective length of strut in a X- Bracing

I would ignore it in strength because the tension capacity is much higher, and that's the failure limit. If this is a serviceability issue like lateral drift, I see no problem accounting for the compression strength.

RE: The effective length of strut in a X- Bracing

JAE I see what you are saying, two columns could deflect toward each other and cause compression in both bracing. WHICH I believe as why to cables aren't used very often for bracing anymore. I honestly don't like setting them as tension only but I conclude I will set my K values 0.7, as one engineer discussed earlier.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources