Bathroom Exhaust Fan Calculation

Bathroom Exhaust Fan Calculation

Bathroom Exhaust Fan Calculation

(OP)
I've been given a arch plan with different types of bathroom arrangements. If I have same area of ventilation( ie volume) but instead of having one toilet I had three in other area, will my CFM different for each types of toilets? What is the rules of thumbs to calculate cfm (l/s) with different basin number?

Thanks
mesi

RE: Bathroom Exhaust Fan Calculation

10 air changes per hour will control bathroom odors.

RE: Bathroom Exhaust Fan Calculation

Try to calculate based on 50 CFM per fixture too. Some standards accept this too.What is the usage any way,if I may Ask?

Thanks

RE: Bathroom Exhaust Fan Calculation

(OP)
They are in two type of projects. One is a childcare and the other one is call center.
Thanks

RE: Bathroom Exhaust Fan Calculation

(OP)
Also how about if our toilet in public place? Is it different with private like an apartment or hotel room?

RE: Bathroom Exhaust Fan Calculation

What code are you designing to? Int'l Mechanical code requires 25/50/70 CFM per fixture depending on several factors, refer to your copy of the code for the factors and how they apply.

Do 2 calculations, one based on code minimum, and Willard's 10 ACH. Use the higher of the 2.

RE: Bathroom Exhaust Fan Calculation

what is your application

RE: Bathroom Exhaust Fan Calculation

15 air change for marine

RE: Bathroom Exhaust Fan Calculation

35 lps asper Ashrae

RE: Bathroom Exhaust Fan Calculation

Per ASHRAE standard 62.1

For Private use: 25 cfm per water closet and/or urinal (normal use)
For Private use: 50 cfm per water closet and/or urinal (heavy use)
For Public use: 50 cfm per water closet and/or urinal (normal use)
For Public use: 70 cfm per water closet and/or urinal (heavy use)


HVAC Zone

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources