Reinforcing steel beam

Reinforcing steel beam

Reinforcing steel beam

(OP)
To strengthen a steel beam that has ready access one side only, I am considering welding in a 35M weldable grade rebar top and bottom, one side of the web only, where the web meets the flange. However that makes it a Class 3 Section, because it is not doubly symmetrical. Can adding lateral braces at close spacing to the compression flange allow the beam to be checked as a Class 2 Section? I am using CSA Standard S16.1.

I know that there are other ways to strengthen the beam, such as welding a tee to the underside, but that requires breaking out the block wall below, spray fireproofing the tee and rebuilding the block wall below.

RE: Reinforcing steel beam

I would be inclined to say no. Why not just size the reinforcing so that it works as a class 3 section?

RE: Reinforcing steel beam

I vote yes. Something like this:

1) Treat the rebar tension and compression as externally applied axial loads applied to the class 2 section. These will induce a torsion on the beam.
2) Design the remaining class 2 beam for said torsion or provide torsional bracing frequently enough that the torsion accruing between brace points is inconsequential. I'd probably go with the latter.

Note that it would not be sufficient to simply brace the compression flange laterally. You'd need bracing that provides effective rotational restraint.

While I believe that this strategy could be employed if desired, I'm not sure that it's the most expedient way to prosecute the design. The class 3 business might be simpler.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

(OP)
I will look at that possibility, but that is a lot of reinforcing, since I would lose approximately 15% in strength in designing as Class 3 versus Class 2. I suppose the welds would have to be sized to develop all that reinforcing? I am trying to increase the beam strength by about 25%, so if it is Class 3, I would have to increase it by about 40%

I think if the beam can somehow be restrained against torsion, that it could be designed as Class 2 section.

RE: Reinforcing steel beam

(OP)
To Kootk - I did not see your response at the time I wrote my response to jayrod12. Thanks for your thought. Very interesting. I will do some calculation and see how it turns out as Class 3. Thanks to you both. I may have a follow up later.

RE: Reinforcing steel beam

(OP)
What is the best way to add reinforcing? A 35M bar top and bottom does not provide sufficient strength. If I use a square bar, say 1½" square, I think it will conflict with the radius of the beam web to flange junction, unless the corner on the bar is coped.

RE: Reinforcing steel beam

What's the bottleneck? Deflection? Straight bending stress? LTB?

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

(OP)
Resisting moment. But it might help if the deflection were reduced too, since the block wall that it supports has cracked. But the bottleneck is mainly resisting moment.

RE: Reinforcing steel beam

Any chance it's deep enough to make sense externally post-tensioning it?

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

(OP)
It is 16" deep and spans 23 feet ±.
I find that the beam reinforced with 1 - 45M bar top and bottom one side only, and checked as Class 3 Section, has 25% more resisting moment (and 43% more inertia) than the unreinforced section checked as a Class 2 Section. So that might work, provided that 45M rebar does come in weldable grade, and that the welds can be developed where we weld it to the flange and web (web = 5/16" thick).

My gut feel is that it is not worth trying to prestress it. What were you thinking...Dywidag bars?

RE: Reinforcing steel beam

Dywidag or something similar. In retrospect, it was lousy advice. Post-tensioning isn't something that you want to do asymmetrically.

45M is one heck of a reinforcing bar. What is the source of the extra load on this beam? Is there a meaty slab above it that might be able to be made to act compositely?

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

(OP)
I see that you are very innovative!
The extra load is from extra thickness of topping that was not recognized as being there when the steel beam was designed and installed in 1994, but which we found out about when we removed it to do structural repairs to the parking garage floor. Actually I don't yet really know the load that the beam takes because the 1994 design was very arbitrary in determining the amount of load that the steel beam would pick up. That is the next thing I will have to look at.

RE: Reinforcing steel beam

If there is solid slab above the beam, as opposed to metal deck and slab, you might be able to core some holes about the beam and post-install nelson studs to make things composite. Let that extra topping work for you!

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

Hate to ask the obvious but can you not add a column or transverse beam lower? I have seen a W-section reinforced with a channel and/or angles before. Amount of steel from the channel was rather significant. I will not say it worked numerically or what the complications were but it was interesting none the less.

One other option, if you cannot make the beam a composite, can you remove the slab and weld a T-section to the top flange. The web if the T welded to Top Flange and then the flange of the T will be then encased in concrete. This will increase your depth for deflection as well as decrease your stress. And it is symmetrical and rather clean to install and inspect. Depending on thickness of concrete you can get a good amount of additional depth (6" slab can make you 5" deeper beam).

PS: And during install you may just relieve all your deadload-preload when the slab is jacked and supported. One more benefit in the composite or the T-reinforcement

T
I

RE: Reinforcing steel beam

(OP)
To Kootk - it is a waffle slab, and there is a block wall above the beam so not the best for making it composite.

To Engineering Eric - I noted in my very first post of the question, that a T added to the bottom of the beam is a possibility. That would be easier than a T to the top, because only need to remove the top course of block, rather all the block wall above the beam, although admittedly it would be overhead welding.

Adding a column is a possibility (I too had thought of that), but would have to brace the top of the column, and cut thru the slab-on-grade and pour a footing, fireproof the column, etc, so not that elegant but certainly worth considering.

I think the 45M bar one side top and bottom is probably as economical as any method, provided the bar can be welded to develop it.

I'll give it some further thought.

Thanks

RE: Reinforcing steel beam

Quote (ajk1)

To Kootk - it is a waffle slab, and there is a block wall above the beam so not the best for making it composite.

The presence of the waffle slab may be a boon here. You should be able to say that at least two of the ribs running parallel to the steel beam non-compositely share the the load applied to the steel beam. And there's a pretty good chance that will get you back to a "do nothing" option.

If you feel like playing along, post a plan showing the ribs in relation to your beam and a cross section through the beam and waffle slab.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

(OP)
How does that get me to a "do nothing" state? Half the column strip width was cut out in 1994, for a length about 10 feet parallel to the span.

Maybe the block wall could be packed up tight to the steel beam soffit and made load bearing, and rely on the 5" slab-on-grade to take the load. The top course of block is likely hollow, so not easy to pack up, but could take the top course out and pour it back as solid concrete up to the steel beam soffit. But pressure on soil under slab on grade probably more than can be justified.

I guess the next step is to make a better stab at what the load the steel beam has to take. May require computer modeling which may be a fair bit of work. Perhaps another way is to figure out how much capacity was lost by cutting out the half column strip and saying that is the strength that the beam should have.

RE: Reinforcing steel beam

My apologies, my mind somehow missed that part :)

If you are concerned about fireproofing and that, i think the removal of your top block (below the beam) is the way to go. Just remove that course, overhead weld, and replace block.

Or maybe add a steel plate 1.5" wider than your flange so you can weld the plate to the beam from above. you seemed to state that there is a gap between the steel and wall, maybe enough for 1/2" plate?. This may require additional compression flange bracing but you can probably make positive connections to the slab...

RE: Reinforcing steel beam

(OP)
yes that is possible.

I a starting to think adding a column and footing might be as good a way as any.

RE: Reinforcing steel beam

[quote ajk1]How does that get me to a "do nothing" state?[quote]

When your steel beam deflects there will be a couple of parallel waffle ribs that will go along for the ride and assume more or less the same curvature. And that means that they'll be sharing the load. Waffle slabs are usually fairly thick so I'm guessing that you might have a pair of 12"-ish continuous concrete beams sharing the load with your 16" simple span steel beam. That sounds like meaningful help to me.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

When I reinforce beams with bars I use round bars, not reinforcing bars - they fit better without the deformations, the end product looks somewhat cleaner, and there are no questions regarding their weldability.
Also, I have found that while smaller diameter bars are easy to weld to the beam, the welds become more difficult with larger diameter bars as you end up welding in a deep groove which is both difficult to complete as well as review/inspect.

Great spirits have always encountered violent opposition from mediocre minds - Albert Einstein

RE: Reinforcing steel beam

Quote (Fish)

I have found that while smaller diameter bars are easy to weld to the beam, the welds become more difficult with larger diameter bars as you end up welding in a deep groove which is both difficult to complete as well as review/inspect.

I've been noodling on this a bit too. I was wondering if one might groove weld the rods to a small sized angle in the shop and then weld the angle legs to the beam in the field (clean fillet welds). You'd loose a little effective depth but gain some extra area so maybe that's a wash. Not sure how one would accomplish a splice if that's necessary.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

Have you thought about adding an angle that toes into the underside of the flange and into the web? It makes a small box of the flange, which should help with potential torsion from asymmetry as well. That can provide a lot of steel, and the angle will be thinner so welding is less of a problem (I imagine with a big bar you have to preheat and that seems like a pain). If you have transverse beams into the one you are reinforcing, I can see it being a problem though...

RE: Reinforcing steel beam

(OP)
to Kootk - the slab is 5" deep rib plus 2½" slab = 5½" total. The beam seems to be centred under one rib. Your suggestion of welding the bars to an angle is interesting, but in the end must still weld the angle to the beam.

to Fishthestructure - very interesting advice about using round bars. I'll keep that in mind.

to structSU10 - what you suggest of making a box of the angles was my very first idea (although I did not mention it here) but our chief engineer was not enthusiastic about it because he said it was not an efficient way to do it (since the centre of gravity of the angles was closer to the beam mid-depth).

New Information:
I was on site again this morning and found that the block wall is not directly under the beam but about 2" clear of it. This suggests to me that the best thing would be to weld a tee section to the soffit of the beam. It is I suppose overhead welding, but is that really so difficult/expensive? The welding would have to be done from one side only, but if a continuous backer bar were welded to one side of the web of the tee before it was lifted into place, then I would think that a full penetration butt weld could be made from one side only. What do you think?

RE: Reinforcing steel beam

Search "Newman beam strengthening". There is a webinar print out document that is very helpful for beam reinforcement.

RE: Reinforcing steel beam

(OP)
To RPMG -- thank you, I will read that. Sounds like just what I am looking for. Much appreciated.

RE: Reinforcing steel beam

(OP)
Can the existing 2.5" of dry pack grout between the top of the steel beam and the soffit of the waffle slab ribs (that run at 90 degrees to the steel beam span, at 2 foot centres) be considered as lateral support for the steel beam? I don't think so, but someone suggested to me that it might.

RE: Reinforcing steel beam

(OP)
And a further question: Should we jack the slab up say 1/4" to take some of the load off the steel beam before welding the new steel reinforcement to the beam, or is that not necessary? Have to be careful not to do more harm than good (such as making more cracks in the block wall that sits on the floor here, although we would monitor the movement with dial gauge. I have jacked up a wood floor about 1/2" a few years ago and it came out quite well, but there were not much brittle materials involved).

RE: Reinforcing steel beam

I picture it as a somewhat complicated problem. Your existing steel has stress/strain in it. If you attach the reinforcing to it, and assume the current stress/strain remains in the member, when it takes more load there is potential for the original member to begin to plasticize much sooner than the reinforcement. But if this happens, the greatly increasing strain in the existing member is restrained by the new reinforcing that may still be elastic - so perhaps it starts to dump extra load into the reinforcing due to the differing strain rate at the interface? Basically though, I think its generally OK to not jack the member due to the large ductility of steel. In the US at least we tend to hold L/600 or 0.3" (the more stringent) for something supporting masonry to help prevent cracking.

RE: Reinforcing steel beam

(OP)
To structSU10 - thanks.Much appreciated. Is the L/600 based on live load or total load?

RE: Reinforcing steel beam

The L/600 applies to whatever load is applied post construction of masonry. Generally I use super-imposed dead load (include weight of masonry) and live load.

RE: Reinforcing steel beam

I'd lean towards not jacking the beam to avoid damage to the existing block wall. And I'd prefer a more positive lateral restraint for the top of the beam. Maybe you can tie back to a few of the perpendicular ribs.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

(OP)
To StructSU10 - ok, thanks. I think I have used that limit as well (I think that may be a published number somewhere). Thanks again. much apprciated.

to Kootk: I agree with what you say. It will apply to a number of beams and may happen at other floors up the building. Anyway, if that is what has to be done, that is what will have to be done, but we will have to check the situation on the other floors. Maybe the beams are not as heavily loaded. It would be interesting if anyone has ever done a load test for this condition to see if the beams buckle laterally.



RE: Reinforcing steel beam

(OP)
How to determine the length of longitudinal weld near the end of a steel T section welded to the bottom of a wide flange steel beam to reinforce it (the stem of the Tee would be welded to the beam bottom flange)? For a steel reinforcing plate, this longitudinal weld length can be taken as 2 times the width of the plate. How would the required length of longitudinal weld be determined for a Tee?

RE: Reinforcing steel beam

America does a good job of this. According to the AISC manual:

1) The attachment beyond the theoretical cutoff point should be adequate to develop the tee's portion of the flexural strength in the beam at the theoretical cutoff point.

2) If the tee will be stressed beyond fy, it's tricky and you can approximate this as the the axial yield strength of the tee.

3) If the tee will not be stressed beyond fy, you can use the formula M/QI.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

(OP)
Kootk:

Thanks. I have some follow up questions:

1. I am checking the reinforced section by limit states design which assumes that the entire portion of the reinforced section each side of the plastic neutral axis (PNA) has yielded. How do I determine if the tee will be stressed beyond fy?

2. For a plate used as reinforcement, there is, in addition to the requirement for the weld to develop fy times the plate area, a requirement that the length be not less than 2 times the plate width (if there is no transverse end weld). For the Tee section, is there only the requirement to develop As x fy?

RE: Reinforcing steel beam

1) Do M/S at the theoretical cutoff point.

2) Rules like that are basically addressing shear lag I think. As such, I'd apply the shear lag provisions for tension members to the tee considering the "connection" to be the portion of the tee extending beyond theoretical cutoff.

What percentage of the span do you plan to reinforce?

For what it's worth, I usually specify stabilizer plates at the ends of the tee. My understanding is that they are required sometimes. Unfortunately, I haven't yet figured out how to assess that need so I've been specifying them all the time.

When using plastic moment capacity, I'll do an extra check of my own. I'll ensure that the reinforcing can develop it's yield capacity on either side of the peak moment with a 2x safety margin. It's not been an issue yet.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

(OP)

ok, thanks. Much appreciated.
I have not yet determined what percentage of the span to reinforce. That's my next step.
If the TEE is welded intermittently along its length (say 2" every 12"), and at each end to develop tee area x fy, can I take it that for service load deflection calculation the inertia to use is the composite section of beam and tee, or is it something less than that due to the intermittent welding?

RE: Reinforcing steel beam

I would take the full section as resisting deflection, accounting for whatever existing displacement is already baked in the cake.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Reinforcing steel beam

(OP)
ok, thanks. Thanks for your help.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources