120 volt parallal/low delta-any advantage to leaving the unusued paralle corners unbonded

120 volt parallal/low delta-any advantage to leaving the unusued paralle corners unbonded

120 volt parallal/low delta-any advantage to leaving the unusued paralle corners unbonded

(OP)
I recently came across a generator used for 120 only. I am working on it for an engine vibration problem but discovered they wired it with the unused corner "unbonded" (best term I could think of). As far as I know it has always worked fine electrically.

On any reconnection scheme I have ever seen (and they are few as this is an uncommon utilization configuration) they are always bonded together at that point. This particular machine has no diagram for this voltage connection inside the cover.

I attached a diagram to explain what I am saying better.

RE: 120 volt parallal/low delta-any advantage to leaving the unusued paralle corners unbonded

It will make no difference under normal operation. The reaction to a winding fault may not be the same.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 120 volt parallal/low delta-any advantage to leaving the unusued paralle corners unbonded

BTW John, you can directly post pictures into your threads now. Use the picture-with-a-circle.

Keith Cress
kcress - http://www.flaminsystems.com

RE: 120 volt parallal/low delta-any advantage to leaving the unusued paralle corners unbonded

(OP)

Quote (waross)

It will make no difference under normal operation. The reaction to a winding fault may not be the same.

What would you envision might happen with a winding fault? Regulator is SX460. Hopefully regulator power would collapse. Which configuration would be more likely to help that happen?

Trying out this picture thing

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources