Solutions for fail concrete of foundation
Solutions for fail concrete of foundation
(OP)
We have poured the concrete of footing in foundation (please see the picture)
the required concrete strength is 28 Mpa but it fail on 22 Mpa,
what are the best solution for such problem
[img
]
the required concrete strength is 28 Mpa but it fail on 22 Mpa,
what are the best solution for such problem
[img
] 





RE: Solutions for fail concrete of foundation
Professional and Structural Engineer (ME, NH)
American Concrete Industries
www.americanconcrete.com
RE: Solutions for fail concrete of foundation
client didn't accept to check and adjust the design for 22 Mpa
we have 2 options
1-remove the footing and reconstructing from the beginning
2-cont the pedestal bars and consider the existing footing as blinding concrete and do the constructing from the beginning also
which one do you thik best
and is there another options
RE: Solutions for fail concrete of foundation
Professional and Structural Engineer (ME, NH)
American Concrete Industries
www.americanconcrete.com
RE: Solutions for fail concrete of foundation