HSS through bolt capacity
I am designing a HSS through bolt connection only subject to shear.
AISC eq. 7-15 and spec. J7 give the equation to predict the bearing strength of HSS through bolt holes. Does anyone know if the bearing capacity given by 1.8FyApb or 1.8nFydt refer to only one side of HSS wall? In another words, the total shear force can be resist by one through bolt is twice of that equation predicts because the through bolt is bearing on two side walls.
RE: HSS through bolt capacity
Mike McCann, PE, SE (WA)
No I am not referring single shear vs. double shear of bolt. I am talking about the bearing capacity predicted by 1.8FyApb. Does that only refer to bearing capacity of one side of HSS wall?
I'm thinking about a truss-type connection though. If you had a through bolt passing through an HSS sandwiched between two gusset plates, where the load was applied evenly to the gussets, that would load the sides equally.
Structural bolts As described in AISC 360 and RCSC, require a steel fill between head and nut. Not a hollow section. Your condition may result in bending stress within the length of the bolt. Not a good idea.
"Hollo bolts" or "blind bolts" are allowed in AISC. However these are proprietary and specifics are provided by the manufacturer. And these are not continuous "through bolts".
Bearing capacity of the wall thickness is one limit state that should be considered.
www.FerrellEngineering.com
Providing fabrication and erection efficient structural design of connections. Consulting services for structural welding and bolting.