Method statement for precast concrete of foundation
Method statement for precast concrete of foundation
(OP)
Hi,
Is there any code specify the main guidelines for preparing the Method statement for precast concrete.
Is there any code specify the main guidelines for preparing the Method statement for precast concrete.






RE: Method statement for precast concrete of foundation
Professional and Structural Engineer (ME, NH)
American Concrete Industries
www.americanconcrete.com
RE: Method statement for precast concrete of foundation
RE: Method statement for precast concrete of foundation
If it's the fabrication then you'll want ASTM C478 for the manholes. For the pipe support foundations I'd simply call out the ACI 318, 304, 308, and 309 specifications.
Beyond that you'll need the loads to be designed for (or the method you want the precaster to calculate the loads) and any other conditions you want considered. Don't get too deep into it because I've seen many specifications over specify the design and fabrication requirements (typically calling out excessive thickness, reinforcement, or concrete cover) so anything you don't specifically need leave up to the precaster.
Professional and Structural Engineer (ME, NH)
American Concrete Industries
www.americanconcrete.com