Trap Seal Primer Alternative
I have run into a situation whereby I am concerned with protecting a tarp seal in a floor drain from drying out.
Drain is in a computer room to collect CRAC unit condensate. CRAC units are scheduled with 0 latent load, actual calculations show 0.1 MBH latent load.
First choice is to use a trap primer and pipe water to the trap; however a suitable source of water is far enough away to be beyond the recommended distance of trap primers (50 feet+).
Second choice is deep seal trap; I have doubts that the drain will receive sufficient amounts of water to maintain the seal (if there was this I wouldn't need the trap primer to start with).
Although there are ways around my problem, I am curious to know if other engineers have used devices such as Trap Guard. Also what has been your justification to allow such a device when IPC does not specifically mention them?
Bill
Bill
RE: Trap Seal Primer Alternative
Have you thought about electronic trap primers where a solenoid opens on a regular schedule to allow a small quantity of water to flow. I specify them where the floor drain is not close to a water line feeding a water closet and I am not likely to get a good pressure drop spike to operate the standard trap primer. They are pricy, ~$800, but will do the job.
I had not thought about using an electronic primer, thanks. Unfortunately, I have similar concern as using a regular primer and that is simply the distance from the trap to the water source. I will have to do some research on that.
Still would like to hear tales where they have been used, both successfully and not.
IPC 2015 now allows "trap seal protection devices) (¶1002.4.1.4).