Metal Stud Shear Wall Straps
Is it customary to specifically prohibit fastening gypsum wall sheathing to metal studs, which pass through shear wall straps?
"It is imperative Cunth doesn't get his hands on those codes."
RE: Metal Stud Shear Wall Straps
DaveAtkins
I don't know of code provisions on this but I will write this requirement into my CFS Specs.
Thanks for bringing this up!
We are not talking about stud compression bracing, but for gravity load-bearing in-fill studs at shear walls, yes, the studs require tight fastener spacing to brace studs. However, theoretically, you want the straps to slide past the in-fill studs to maintain truss action. I am just wondering if it really matters in this situation - what is the worst that could happen?
Or does this refer to metal bridging?
EIT
www.HowToEngineer.com
The fastening of the gypsum to the studs - the installer isn't going to care whether screws grab the straps (shear wall straps) while fastening to the in-fill studs.
[Mac] I understand the intent for the straps to slide past. But, the only remote guarantee we could depend on is that the gypsum installer DOES fasten to one of the straps.
Assuming this is the (likely) case, what is the worse case scenario that would result? Further assuming the infill studs are a lighter gage than the chord (or anchor) studs or gussets (I'm assuming you have gussets top and bottom), if it were one, isolated in-fill stud, wouldn't that particular (non-structural & non-critical) stud fail locally, by ripping the stud chord, and, thus, be of negligible (if any) harm to the wind system?
Now, if the installer happened to connect with multiple in-fills, what is anyone's opinion of the result? I'm curious.
Further, as BUGGAR suggested, I also will consider including this into my spec as needed. However, [Mac], (maybe I'm overanalyzing), did you originally mean to inquire about fastening gypsum screws to the strap rather than the studs? The gypsum HAS to be fastened to the studs. I would consider, in a spec, prohibiting the gypsum fastener to the diagonal strap to cover your liability.
I must be missing something here. I think if you check the rupture strength with net area vs yielding and gross area. The yielding & gross area will govern with the such a small hole. Plus you the gypboard fastened to the studs is like a bonus shear wall sheathing (sorta).
EIT
How do you get anything done? (lol)